Hello All,
just rewired a kitchen, 2 new circuits...
A socket radial circuit...And,
There is a double oven, on one side of the kitchen, and a hob on the other side, I wired this as its own ring circuit, on a 32amp breaker..
I put the double oven on a socket, and the hob with a low level cooker unit, I never put an isolator for this, can somebody point out if this is needed...thanks
 24 February 2014 08:01 PM
aligarjon
Seems a strange way to rewire a kitchen after going to all that trouble. Why not just do it properly. What size is your radial ?
Gary
 24 February 2014 08:05 PM
peteTLM
why did you put the double oven on a socket if its on a dedicated circuit? and why a ring for 2 points? No 4 or 6mm available in your part of the world?????
What hobs can be run off a ring circuit????
What size are the hob and the oven then?
 24 February 2014 08:07 PM
TopTrumper
Gary, radial is 2.5mm, not really supplying much...
I know what you mean, reason for this was believe it or not, ease of cable from one side of wall to the other, proper concrete walls and floors, i always put 45amp dp switching, but in this case, it never went in....
Its on its own mini fusebox, with dp isolation, so i ask again, is it needed?
 24 February 2014 08:13 PM
TopTrumper
Pete, have a look at follow up answer...I have wired hundreds of cooker radials, but this particular one went in as a ring, without boring you why it went in like that, it just did, its just a bog standard double oven and 4 ring hob
 24 February 2014 08:26 PM
Crazycolours
Hi TT,
Yes, it is needed as a matter of good practise and also 7671 - 537.2.1.2. Of course this will probably lead to a debate about the ambiguity and interpretation of the Regs. But, in my defence it is also in the OSG page 45 - 5.1.1. iii. for every item of equipment.
Regards, C.
 24 February 2014 08:29 PM
TopTrumper
Anybody?
I always put in an isolator without fail, and i know about the 2 metre good practice rule, but fusebox is 4 metres away, im just wandering if i can get away with it, I cant see anything in book that says you must have it.
 24 February 2014 08:31 PM
TopTrumper
crazycolours i have read page 45, and like i say, there is dp isolation on its own fusebox. it does not mention anything else
 24 February 2014 08:33 PM
peteTLM
So the 4 ring hob is on a 2.5mm ring??
The others replied while i was typing..........typing slow..
Cooker isolation has been changed from mandatory (as it were) to engineering preference, which means you dont have to bother. I always do it, everyone else still does it, but i dont think anyone is going to get upset on this one, as have you said, the CU can be used
 24 February 2014 08:42 PM
TopTrumper
Pete,
there is a low level cooker unit wired as a ring, hob will be fed by 6mm from this..This circuit had to get clipped under ceiling, on proper concrete, 6mm cable would just not cut it...
Wish these fookin guidance books were not so feckin vague...
 24 February 2014 08:49 PM
Crazycolours
Pete,
I never knew that - where and when was that written?
Regards, C.
 25 February 2014 06:01 PM
SKElectrical
Cooker isolation has been changed from mandatory (as it were) to engineering preference, which means ..... the CU can be used
Nicely put. I agree. It's engineering preference here.
For what its worth I always reckon a 20A radial just doesn't cut it for socket power in kitchen.
 25 February 2014 07:53 PM
dickllewellyn
I must say I'm not convinced about a hob on a 2.5 ring! What sort of load wil the hob be fully loaded? Concentrated on one part of a ring? How was it easier to install two 2.5 t&e than to install one 6mm t&e?
Richard (Dick)