Topic Title: Continuity of CPC. Continuity test method 1
Topic Summary: Size of the temporary link
Created On: 20 February 2014 10:30 AM
Peewee
Hi, Are there any notes on the size of the bridge from line to protective conductor?
I can't see anything in my books, my gut feeling would be to use the same size as the line conductor from the circuit i'm testing?
Can anyone offer any definitive answers on this?
Pete
 20 February 2014 10:35 AM
marclambert
My idea of a temporary link is to remove both conductors and connect together. Never use link as per drawings in OSG and GN3. They can and have been forgotten.
Solves your question too?
Marc
 20 February 2014 10:42 AM
What is the accuracy of the instrument ?
What impact on the measured results would say the variation between 1.5mm2 or 2.5mm2 copper of say 150mm long have - what would that be as a % of the measured test result?
Would a change in temperature have more or less of an effect ?
In essence, how definitive is the test result anyway ?
If I suggested, that it did not exceed 0.05 Ohm would you find that credible
 20 February 2014 10:53 AM
marclambert
I suppose if you really wanted to use a link it's csa wouldn't matter. Just null it out when you null the leads.
Simples!
But still don't do it
 20 February 2014 02:00 PM
dickllewellyn
I tend to test one at a time by outing the line conductor into the earth bar. It's one of those things that everyone will have a different method!
Richard (Dick)
 20 February 2014 02:27 PM
When i'm doing c/unit changes I find the lever type Wago's very useful especially when cross-connecting L & E for ring tests etc.
 20 February 2014 03:02 PM
marclambert
Me too Dave,
hold em together with your teeth even, anything but links.
If you leave a link in a BS88 DB and energise, for sure the fuse will blow but if you're stood in front of the board on top of steps at the time......a step backwards could well hurt.