 17 February 2014 11:07 PM
User is offline View Users Profile Print this message



kirchoffs

Posts: 180
Joined: 08 February 2010

Got a call from a regular client today. Someone had been in at the weekend and made off with all the AC outdoor units,they just cut the pipes and cables.
So could i call round and "make safe". When i got there what really caught my eye was the state of the SY cable used to link to the internal units which virtually all of the clear outersheath was perished on all 17 units. what was left was very sticky .

I can only assume it was a reaction from the sun's uv.
I've seen SY used for this purpose dozens of times , but not so much lately, Perhaps this is why? i will have to ring Batt calbles just out of curiosity it see if SY is suitable for external use.

Has anyone else come across this?
 17 February 2014 11:20 PM
User is offline View Users Profile Print this message



intrinsic4225B

Posts: 1623
Joined: 30 September 2004

I would have expected exposure to sunlight and in particular the UV portion of the spectrum to cause embrittlement and cracking rather than stickyness, but I suppose it could be plasticiser migration or some similar process?
 18 February 2014 07:55 AM
User is offline View Users Profile Print this message


Avatar for leckie.
leckie

Posts: 1864
Joined: 21 November 2008

Here is a bit of information
http://www.voltimum.co.uk/arti...ated-yy-and-sy-cables

And here is a bit more from Eland that mentions outdoor use
http://www.sycable.co.uk
 19 February 2014 06:53 AM
User is offline View Users Profile Print this message



kirchoffs

Posts: 180
Joined: 08 February 2010

Cheers leckie,, Thats a big no then.
You learn something new eveyday in this game.
 19 February 2014 07:42 PM
User is offline View Users Profile Print this message


Avatar for OldSparky.
OldSparky

Posts: 592
Joined: 28 June 2011

i connected a load of motors outdoor with SY wish i hadn't now.. all starting to go funny..

Maybe HO7 would be a better alternative
 19 February 2014 09:48 PM
User is offline View Users Profile Print this message


Avatar for leckie.
leckie

Posts: 1864
Joined: 21 November 2008

I don't know why SY is seen so often on air con units, etc. The clear cover goes brown and brittle after a short time outdoors, it's not classed as an armour or any use as a CPC, so what's the point. Use Hi-tuf. Easy to install and doesn't go brittle. If you need armour use SWA.