keithredpath
We have numerous circuits of underfloor busbar systems supplying 16 Work Stations each. Each work station has a PC and a VDU.
The supply cables are 10 mm SWA.
All the MCBs are 20 amps.
Most are Type Cs (Some are Type As)
The problem is after a power failure, it takes numerous attempts to get the MCBs to come back on. They spark and arc extensively.
I will recommended upgrading the MCBs to 40 Amps (Type C) but I still have a feeling the inrush currents are the problem. Is there any way to measure these inrush currents, so I can then recommend type D MCBs if this is found to be the problem. The earth loop impedances are all below 0.33 Ohms.
keithredpath
 09 December 2013 10:16 PM
MickeyB
32A Type D is standard for commercial jobs....... you could use Type C if you kept the load down. ...
16 is way too many PC's...... limit to 6 or 8 or so..... earth leakage/ surge etc. ...
Unfused taps? with 4mm tails to desk distribution module?
 10 December 2013 07:49 AM
Ricicle
What type of VDUs are they ?
 10 December 2013 08:38 AM
gkenyon
Many manufacturers of PCs and associated equipment, that are intended for commercial / industrial use, supply this information (often on-line) as a matter of course these days, for precisely the reason you state.
If no information is forthcoming, then the following "rule of thumb" might be useful for maximum inrush currents:
- Flat-Panel Monitors up to 322 : 15 - 20 A inrush
- Small SMPSU (<80 VA): 10 A inrush
- Larger SMPSU (or PCs) 80 - 650 VA: 20-25 A inrush
- Heavy SMPSU >650 VA (or Server, each input if more than one PSU): 35 A inrush.
UNLESS the equipment is old (before around 2003), in which case even 240 VA SMPSUs sometimes had inrush currents in excess of 120 A !!!!
You need to assume that the maximum inrush current will flow for 20 ms, and (I probably don't need to add) that whilst for tripping times in fault, we use the "worst-case" of the operating curves for OPDs (i.e. for mcb's Type B 5 In, Type C 10 In, Type D 20 In), when looking at inrush, we need to consider the "best case" (i.e. for mcb's Type B 3 In, Type C 5 In, Type D 10 In).
Because a real OPD will operate somewhere between the "worst-case" and "best-case", if your calculations show something just above the "best-case", swapping the OPD is often a way of stopping a nuisance-tripping problem caused by inrush currents.
Measuring inrush currents is not easy, best left to the manufacturer or specialist test lab.
Inrush currents aren't just a problem for power-on, they can also be a problem with temporary power dips (brown-out) or surges, particularly with IT equipment, as they are often a result of charging large capacitors in the PSU.
And finally - there is another (some might say, a technically more "elegant") solution: use a fuse instead of an mcb! Simply because the fuse doesn't have the discontinuity in its operating characteristic as mcb's do: where in the mcb the magnetic element takes over from the thermal element.
Principal and Proprietor,
G Kenyon Technology
Web-Site: www.gkenyontech.com
 10 December 2013 12:59 PM
Another approach is to time-delay on switch on, each load with a different delay, so you're only having to deal with the surge from one item (+steady load from the rest) rather than sum of all the surges at the same time. There are readily available 'sequential start' power distribution units (PDUs) for rack mounted equipment from various manufacturers and some UPSs have a programmable delay before switch-on when power returns - all to address this very problem. If you've a distributed system you can achieve the same effect with an on-delay timer at each outlet (floor box say), each set to a different delay.
 10 December 2013 05:07 PM
gkenyon
Andy,
Just to add that the delay-starts are OK for solving the power-on tripping (as per original question in the thread), but may not help if tripping is also occurring during brown-out and surges.
And also add that the use of fuses instead of mcb's of course has drawbacks from an operational perspective, if indeed they can be retrofitted in the relevant DBs?
All due to progress ;-)
G Kenyon Technology
 10 December 2013 06:02 PM
Wouldn't you need to consider a crest factor as well Graham ?
ie the maximum inrush current (I@20ms) that an MCB will carry is :
In x minimum tripping threshold for MCB Type x crest factor
So for say a 20A Type C in the OP
20A x 5 x 1.414 = 142A
Say 6 No desktop PC's or 2 - 3 servers (max no of SMPS).
It's hardly suprising a 20A Type C is tripping with 16 PC's connected.
 10 December 2013 10:49 PM
gkenyon
OMS,
Good point, but I think the answer needs to be ... I suppose it depends.
I suspect that inrush currents quoted by many manufacturers may be divided by the Crest Factor, which may be different from SQRT(2), to make them appear lower in the first place: not sure it's "regulated" by a standard.
G Kenyon Technology
Edited: 10 December 2013 at 11:00 PM by gkenyon