Topic Title: Flickering Lights.
Created On: 02 December 2013 09:01 PM
JonSteward
Came across an unusual situation.
Lights in a remote property flicker, only slightly, when dimmed.
This is on several tungsten filament circuits, mains halogens and low voltage.
Looks like an external issue so now talking to neighbours.
Any other ideas?
 03 December 2013 04:36 AM
DOUGIE1000
Bad join somewhere, does table lamps do it?
Dougie
Power Plus Electrical.co.uk
 03 December 2013 09:20 AM
If table lamps do it probably poor connection at the meter, cut-out or c/unit? (most likely neutral)
 03 December 2013 11:16 AM
What type of dimmer is it ?
 03 December 2013 11:25 AM
Any other ideas?
Maybe a 'disturbing load' somewhere in the neighbourhood, but the varying voltage is less noticeable when the lamps are at full brightness? Maybe.
What sort of frequency is the flicker? is it the same across all circuits? Are several different types of dimmer involved? Has it always done this or has it suddenly started happening with no changes to the installation?
 03 December 2013 06:14 PM
JonSteward
Thanks for the replies.
The dimmers are Varilight V pro (which have various software incarnations), I swapped one for a vintage dimmer from my spares box with no significant difference.
This only became apparent once the winter months kicked in. (10 month install).
The flicker is random and not regular. Seems to step up then down but only slightly. You really have to stare at it to notice.
 05 December 2013 12:24 AM
SKElectrical
the lights in my house have done this since I moved in 2 years ago. I have double checked connections at c/u and meter, including dno side. Both light circuit upstairs and light circuit downstairs affected. I haven't tried a desk lamp yet because I refuse to buy an incandescent bulb. Only a few GU10s left which are most noticeable, the rest of my house is cfl or led which seem unaffected.
GU10s flickering on dimmer is just as noticeable as when at 100%. I have not asked neighbours if they experience similar problems.
Without wiring in a desk lamp with incandescent bulb directly to pre cut out, there are a host of possibilities.
 05 December 2013 09:53 AM
williamjack
This can be due to bad connctions.
 05 December 2013 10:17 AM
Colin Jenkins
Hello Jon.
On a "remote" installation, the property is probably fed by a long overhead service from a pole-mounted small transformer which can present a relatively high source impedance. Electrical loading on/off in the property can thus cause a voltage variation and a consequent disturbance to the established lighting levels. For some reason, this seems to be much more apparent to the human eye perception on low lighting levels than it is at full levels. My own property suffers from this, it's been there for about fifteen years, it's only noticeable on dimmed lighting, and it's not loose connections.
If you get called back it would bee wise to check all the accessible circuit connections to eliminate a loose one, but it could be like the above that cannot be easily solved.
I hope this helps.
Colin jenkins.
 06 December 2013 06:53 AM
JonSteward
My gut feeling is external.
Being rural there maybe farm equipment on the same line. I'll try to locate the TX next time, might give some clues.
I'll also check the internal loadings and connections.
Thanks again
 06 December 2013 06:03 PM
burn
I can back up what Colin says. Until recently I was in a similar situation, until Western Power upgraded the network, making us part of an LV ring main with the cables underground.
Previously I measured 223v at best and often down to 218v.
Now I have a steady 230v.
Except about 2 hrs ago that is, when like half of Lincolnshire was subject to a problem on the grid, at West Burton power station.
I was interested to note my CFLs, the TV,DVR and Mocrowave all worked at 180v. If the 12v downlights had not been dim I would not have known.
burn