Ampman

Posts: 1009
Joined: 06 February 2006

Evening ,

Started testing a job today where the rcbos test buttons dont operate the trip ,

Yet the rcbos trip fine when tested , In my eyes this is a fail ?

Just want to see what others feelings are ?

Cheers
 28 October 2013 08:38 PM
User is offline View Users Profile Print this message



ady1

Posts: 766
Joined: 19 April 2005

Memara 2000 by any chance ?

Regards
Ady

-------------------------
Resistance is futile.
 28 October 2013 08:42 PM
User is online View Users Profile Print this message


Avatar for stateit.
stateit

Posts: 2161
Joined: 15 April 2005

Or Chint, circa 2011.

-------------------------
S George
http://www.sg-electrical.com
 28 October 2013 08:42 PM
User is offline View Users Profile Print this message



Ampman

Posts: 1009
Joined: 06 February 2006

MEMSHIELD 2
 28 October 2013 08:46 PM
User is offline View Users Profile Print this message



largelunchbox

Posts: 365
Joined: 06 July 2008

fail
 28 October 2013 08:49 PM
User is offline View Users Profile Print this message



ady1

Posts: 766
Joined: 19 April 2005

Thats what i meant... (its late)
Hope you find out, cos i never have.
I've known it happen to about 5.
Also, some don't work on 1x Ian but do at 5x
Also, the test button can trip upstream too.
Needless to say - I dont specify them.

Regards
Ady

-------------------------
Resistance is futile.
 28 October 2013 09:15 PM
User is offline View Users Profile Print this message



Ampman

Posts: 1009
Joined: 06 February 2006

Thought it should be fail ,

There about 50 quid to buy , ive got 3 already fail , & about 30 more to test
 28 October 2013 09:20 PM
User is offline View Users Profile Print this message



prophet

Posts: 212
Joined: 09 October 2011

Are they the rcbo units that retro fit onto an MCB?
 28 October 2013 09:43 PM
User is offline View Users Profile Print this message



daveparry1

Posts: 6169
Joined: 04 July 2007

Are the white leads connected?
 29 October 2013 11:41 AM
User is offline View Users Profile Print this message



Delbot321

Posts: 77
Joined: 06 November 2012

If the buttons not working I would give it a C2 fail as this prevents the user from doing the required quarterly checks on them.

If they fail on x1 or x5 this is a little more complicated to decide on. If the RCD is being used to provide protection against shock and forms part of the ADS (Automatic Disconnection of Supply) protection then I would give it a C1 and also issue a warning notice to the client. If the RCD is only providing ADDITIONAL protection (cables in walls, fire, equipment used by ordinary persons, sockets outdoors ,etc) then I would give it a C2 fail.

Hope this helps.
 29 October 2013 11:16 PM
User is offline View Users Profile Print this message


Avatar for dg66.
dg66

Posts: 1670
Joined: 11 January 2008

Originally posted by: Delbot321

If the buttons not working I would give it a C2 fail as this prevents the user from doing the required quarterly checks on them.



If they fail on x1 or x5 this is a little more complicated to decide on. If the RCD is being used to provide protection against shock and forms part of the ADS (Automatic Disconnection of Supply) protection then I would give it a C1 and also issue a warning notice to the client. If the RCD is only providing ADDITIONAL protection (cables in walls, fire, equipment used by ordinary persons, sockets outdoors ,etc) then I would give it a C2 fail.


.Hope this helps.



Cant really be a C1 , as its not immediately dangerous.

-------------------------
Regards

Dave(not Cockburn)