Topic Title: kVA - Amps, Three phase - Formula
Created On: 02 October 2013 09:06 AM
paultrimble
Hi all
I have been asked to advise on supply conductor size for a sub distribution supply. The power I have been told is 10kVA, 400V.
I am used working with Kw power but not really for kVA.
Can someone clarify if my formula is correct please?
I(A) = 1000 × S(kVA) / (?3 × VL-L(V) )
Therefore - 1000 x 10kVA = 100000 / (1.732 x 210V)
= 27.49Amps?
This is where I get a little confused, if I transpose kVA to KW my result is different ; -
P(kW) = S(kVA) × PF
10*0.95 = 9.5kW
Therefore using formula for 400V kW - Amps I get 14.43Amps?
Hopefully that's not to confusing,
Cheers
Paul
 02 October 2013 09:07 AM
paultrimble
Just noticed a typo - 10000 not 100000
 02 October 2013 09:59 AM
As a sanity check, I tend to think about it the other way around - 10kVA from a 400/230V 3-phase supply is the same as three 3.33 kVA single phase loads - so 14.49A per phase (at 230V).
 02 October 2013 10:03 AM
paultrimble
Cheers Andy, I noticed I used 210 line voltage instead of 400V for some daft reason
Your reasoning makes perfect sense
 02 October 2013 11:04 AM
Parsley
I divide KVA/692 if using 400V (1.73 x 400) and by 718 (1.73x 415)for 415V to get current.
10000/692 =14.45A