Topic Title: RCD causing false Zs readings
Topic Summary: Advised by MK to by-pass RCD for test
Created On: 20 July 2013 09:25 PM
1 2 3 Next Last unread
rslane
Low Ze and low r1+r2 but Ze like three times the sum of them.
The only extra items in the circuit are the items in the consumer unit.
So I measure loop impedance before and after the 63A RCD of the Sentry CU. Supply side 0.34ohm; load side 1.10ohm. (Measured with Kewtech meter in anti trip mode.
So I ring up MK and say serrious problem with their RCD.
They say no, "its the electronics in the modern RCDs" and that I should turn the RCD off and by pass it for the Ze measurement.
So I try this and now get a figure of 0.41 ohm when I connect meter at the end of this botched circuit.
I can't say I am at all happy with this way of testing.
Apart from the extra work and the risks from stuffing temporary links in the CU, it is not a test of the complete cicuit. What if the RCD did actually have high reistance contacts? Of course that wouldn't ever happen, would it? I mean they are not 100A main switches! (I assume that was the reason for the recall.)
 20 July 2013 10:20 PM
Are you getting mixed up between Zs readings and Ze readings or am I misunderstanding your post? Take both readings from the primary side of the main switch, one with earthing conductor connected, one with it disconnected.
 20 July 2013 10:34 PM
Sorry rs lane, I think I was confused reading your 1st sentence. I think you said Ze the second time when you meant Zs? Well again, measure prior to the rcd.
However I have noticed that some rcd's give weird IR readings. I know your supposed to isolate them, and they may be vulnerable to testing but, some are not. Are you using no trip and standard earth loop impedance tests? The no trip test often gives higher readings on my meter.
 21 July 2013 03:43 AM
rslane
Yes, I had meant to say in first sentance that Zs was three times higher.
I had measured Ze at input to main switch with only earth to supply cable connected. Then measured r1+r2 for cooker circuit. Both readings good and low. But on connecting everything up, the overall loop impedance, measured at cooker control panel terminals was about 3x the sum of the two parts and too high and failing.
To investigate I measured loop impedance at supply terminals to RCD and then at RCD output terminals. If the test meter is giving true readings they should be almost the same as the only extra imedance in the circuit will be the contacts in the RCD. If they are not very low resistance it will overheat on full load. 63A x 63A x anything other than low contact resistance = very hot RCD.
Now what MK tell me is that even with anti trip technology I will get false Zs readings when measuring through the RCD.
 21 July 2013 07:56 AM
ssohnoherewego
I encounter this all of the time. Just put your calculated values onto your test sheet and state why it was calculated.
 21 July 2013 08:46 AM
If you look at a standard rcd circuit diagram, usually printed on the rcd, it never shows "fancy" electronics. Different manufacturers much have different circuit electronic arrangements I suspect. So some, in this case MK, may give different test results. I haven't noticed differences as large as rslane has described on Crabtree, control gear, or Hager that I have used. However I have noticed that when doing IR tests with L/N connected together to earth, that sometimes I get a low reading across the rcd, with the rcd off. If I do the same test with the rcd out put disconnected the reading on the circuits is OK. But it doesn't always happen. I have put this down to electronics with the rcd. By the way, who records the rcd as being an item vulnerable to testing on EIC's?
 21 July 2013 12:26 PM
perspicacious
"By the way, who records the rcd as being an item vulnerable to testing on EIC's?"
Everyone who has read 514.9.1 (iv) and looked at what must amount to 5% of the page area of p402..........
BOD
 21 July 2013 12:47 PM
Legh
For a slightly different reason.
When Loop testing using an LT5 through a BS 4293 RCD I always connected jump leads so I could get a reasonable Zs. Now I test either side and add the values together.
Coupled with a RCD time test and a ramp test to ensure, to some degree, a level of correct operation.
Legh
de-avatared
 21 July 2013 01:53 PM
rslane
"use calculated values"
Thanks. It may be what we have to do for the moment.
But I am still not happy that the manufacturers have pushed the electrician into a corner by developing a device that makes one the basic safety tests impossible with industry standard instruments.
So whats the proper long term solution?
a) Redesign of RCDs to make them testable in circuit with existing instruments.
b) Redesign of RCDs to have a foolproof test override facility thats lets us do an impedance test of the complete loop.
c) New test equipment that will give the correct answer for the as installed complete circuit.
d) Get the regs amended to say we don't need to do the test.
Now I can't see a) or b) happening any time soon, the manufacture's would need considerable preasure on them to spend that sort of money. And in any case what of all the "untestable" units in sercice.
And I can't see d) happening, nor would I advocate it. It would be the thin edge of the wedge. Next step, use calculated values for everything and throw away the test equipment. In theory if we have designed the instalation to the book it will be perfect. But then the unexpected happens and what we think we have is not what we actually have. And so we test to make sure. A calculated value for Zs fails to find a high resistane RCD, a high resistance MCB or a poor connection in the consumer unit. But then manufacurers never supply faulty equipment, none of us ever makes a poor connection and nothing ever detioriates!!
So in my opinion there still needs to be a way to test.
To me it is starting to look like c), new test equipment and yet another cost for the electrican to pass on to the customer who won't pay and will use a cowboy.
WHAT'S THE ANSWER?
 21 July 2013 03:12 PM
weirdbeard
Originally posted by: rslane
WHAT'S THE ANSWER?
411.4.9?
 21 July 2013 04:05 PM
Are you absolutely certain that the MK RCD is NOT ADDING TO THE IMPEDANCE OF THE CIRCUIT?
Are you absolutely certain that the high figure is not the TRUE FIGURE?
If so can you explain to me why?
Andy
 21 July 2013 04:31 PM
rslane
You are quite right - it might be adding to the impedance and the reading might be right. That is why I am still worried.
 21 July 2013 04:33 PM
rslane
PS sorry to be so impersonal on this site. rslane = Bob.
 21 July 2013 04:40 PM
Originally posted by: leckie
. . . I have noticed that some rcd's give weird IR readings. I know your supposed to isolate them, and they may be vulnerable to testing but, some are not. . .
All RCDs are vulnerable to IR testing. Usually an RCD will be connected such that the supply to its internal circuitry is disconnected when it is off. The test resistor and switch is usually wired such that the "load side" phase is connected to the "supply side" neutral. If you connect it the other way round, operating the test button may energise the neutral of the installation and leave its internal electronic circuitry energised.
 21 July 2013 05:03 PM
rslane
By the way Andy I see you post far more than I do on the forum but it looks as if we both joined on the same dayy, 18.1.03!
Regards, Bob
 21 July 2013 06:02 PM
Sorry, I know that RCD's are vulnerable to testing if they are not switched off, what I am saying is that some are vulnerable even when they are switched off I think, as some read even when off. I'm talking about doing rcd output lives linked and tested to earth. I just wondered why some are and some are not?
Why I mentioned the recording of rcd's being included as vulnerable on EIC's is because I do, and yet I very, very, rarely see it on the many certificates I see issued by others.
 21 July 2013 07:45 PM
weirdbeard
Hi BOD, I can't see how an RCD is vulnerable to damage from typical testing, how else are you supposed to fill in the schedule of test results RCD columns?
 21 July 2013 08:37 PM
Cheeky monkey weirdbeard
 21 July 2013 10:22 PM
"By the way Andy I see you post far more than I do on the forum but it looks as if we both joined on the same dayy, 18.1.03!
Regards, Bob"
First off I spend hours talking to myself, secondly I suffer cabin fever on account of working long hours on my own
 22 July 2013 07:13 AM
davezawadi
RCDs should be designed to deal with mains spikes (and therefore insulation testing) without damage. If I ever found a make which failed permanently on a 500V test I would be at the manufacturer very hard indeed (and I haven't). It is imperative that safety devices (such as RCDs) can survive in the real world because any failure is not visible yet leads to significant danger to the user.
It may be that some RCDs give low readings of IR, but they should never be subject to failure. Whoever wrote that bit of the regs BOD certainly did not intend to include RCDs, and in my view any accessory or appliance which cannot withstand a 500V test without damage is not fit for purpose. Some poor quality items may not withstand 500V between live and neutral, but are likely to fail prematurely as a result.
There is history in this, as over voltage protection, surge suppressors etc are fairly new components (only about 25 years) so have not fully arrived in the vocabulary of product design in some areas, and can be left out to reduce costs with immediate benefit to the manufacturer, until the complaints roll in!!
David
BSc CEng MIET
IET » Wiring and the regulations » RCD causing false Zs readings