Topic Title: Scalemaster showers
Created On: 03 July 2013 08:18 PM
frspikeyhead
Fitted a 9.5KW scalemaster shower which was replacing an existing 8.5KW scalemaster which is on a 40mcb and a 6M run of 6mm. The shower only pulls 34A on max and doesn't exactly get hot on full power. Any ideas other than faulty?
 03 July 2013 08:37 PM
perspicacious
What Zs did you measure?
BOD
 03 July 2013 08:39 PM
Probably have too good a supply of cold water! If there's a service valve in series try throttling it back a little bit,
 03 July 2013 11:06 PM
AncientMariner
Voltage on-load?
Cheers!
Clive
 04 July 2013 09:03 AM
I agree with Clive. What is the voltage at the terminals in the shower when it is running - it is possible that volt-drop on your 6mm supply cable is the issue here!
 04 July 2013 09:34 AM
I wouldn't think thats very likely on a 6m run of 6mm t/e Alan?
 04 July 2013 09:39 AM
Parsley
It's going to be below 210V at the load end to only be drawing 34Amps.