Gas bottles are sitting outside on the ground with a chain tied to wall to stop them falling over.
Dougie
Power Plus Electrical.co.uk
My mission is to live as long as possible......so far so good!
 17 June 2013 09:20 PM
daveparry1
I wouldn't have thought it necessary Dougie, the bottles are connected by rubber pipes to the regulator I guess?
Dave.
 17 June 2013 11:55 PM
baldelectrician
No if they can't introduce a potential
Yes If they are connected to a copper pipe inside that distributes the gas to appliances (such gas appliances may have a gas ignition or be sitting next to class I appliances)
baldelectrician.com
 18 June 2013 10:25 AM
AJJewsbury
Would that allow the pipe to introduce a potential into the installation?
 18 June 2013 07:39 PM
AdrianWint
Wouldn't this be more a risk of exporting the 'earth' outside of the installation & hence the equipotential zone ..... aka the garden tap problem????