Hi,
Part of a lv sub-main cable was cut & stolen. We have decided to install an isolator between the new cable supplied from the switchgear, and the rest of the existing cable that feeds the DB.
Never come across this..how do I calculate the volt drop? Should they be two separate cables or calculated as one? Should they be the same size etc? Any regulations reg. this?
Sorry if I haven't made it clear...any help would be appreciated. Thanks.
 16 May 2013 12:49 PM
Assuming that the new cable is the same c.s.a. etc as the old one, it doesn't matter - you can calculate it either way and the answers should add up the same. If the new cable is different from the original, you'd have a different mV/A/m figure to work with, so you'd have to do it as two different sections and add the results together.
 16 May 2013 12:52 PM
perspicacious
Did the last PIR or EICR carried out on this cable before it was stolen raise any concerns about it being the incorrect size?
BOD
 16 May 2013 01:12 PM
calumbtw
Ok, thanks for that Andy
BOD
Nope not that I am aware of.
Thanks for the help!