Topic Title: En-Suite .
Topic Summary: Care Home .
Created On: 14 May 2013 07:28 PM
Ampman
Got to install a light in a en-suite that will have a fixed shower installed .
Light will be out of zones ,
Do i still need an rcd ?
thinking yes , but the care home has about 40 other en suite rooms without rcd protection .
So i thinking i will rcd mine & advise on the others .
 14 May 2013 07:42 PM
sparkiemike
Are you just replacing a fitting, or is there new cabling for a new light?
If it is the latter then no need to RCD, otherwise I would say you need RCD protection as well
 14 May 2013 07:54 PM
Or you could take the approach of "all circuits of the location" it's nothing to do with zones - do yours and then they know whats required for the other 40 en suites as well
Other way round ?
 14 May 2013 08:46 PM
Ampman
yes new cable required ,
nightmare to rcd if im honest .
 14 May 2013 08:56 PM
dg66
Fit a class 2 fitting and note a deviation from the regs and note that a class 2 fitting provides better protection than an RCD.
Dave(not Cockburn)
 14 May 2013 09:14 PM
Ampman
very good idea ,
can i really get away with that ?
 14 May 2013 09:34 PM
RCD FCU above en-suite door ???
 14 May 2013 09:46 PM
dg66
very good idea ,
As the designer you can do what you like as long as you can show that your deviation provides equal or better measures of safety as would be afforded by strict compliance, i would 'nt bother with an RCD for SELV light fittings either as they also provide better protection than an RCD.
Its your call as you are signing the paperwork.
Dave(not Cockburn)
 14 May 2013 10:07 PM
Double insulated, selv, good ideas.
Reminds me of recent posts regarding what boxes to tick!
 15 May 2013 09:27 AM
Does it really - the fitting may be safe, instrinsically, but there is a reason why BS 7671 discusses all circuits of the location - note the distinction between all circuits and the concept of the appliance, accessory, luminaire or outlet.
 15 May 2013 10:20 AM
Ooh, I think I can play Devil's Advocate here
The requirement for 30mA RCDs is in reg 701.411.3.3 - i.e. it's a modification to section 411 of the main regs. Section 411 is about ADS only. If it was elected to design using section 412 entirely instead (double or reinforced insulation), then the requirement for 30mA RCDs wouldn't apply. As it's a care home it might be under effective supervision and so 412.1.3 could be satisfied (provided no-one wanted to use LSCs etc), allowing double insulation to be used as the sole protective measure (for that circuit at least).
 15 May 2013 11:17 AM
Of course Andy, why am I not suprised - but that assumes that the original designer was adopting double insulation as a sole means of protection. To retrofit a DI solution would need knowledge of the wiring systems employed - class 2 luminaire on a metal conduit enclosed circuit with a CPC present (but not terminated at the luminaire) wouldn't and couldn't be DI so the RCD would be required.
Then we look at supplementary bonding being present.
In very specific circumstances DI would make the installation of RCD's nugatory - I designed such a system for chemical washdown showers for emergency use (as they don't fall under Section 701) - I strongly recommend we don't suggest to anyone that DI systems in a care home should even enter into the design thinking, in practice though - I can't ever see there would be that degree of supervision.
 15 May 2013 03:43 PM
dg66
IMO it does, an RCD wont stop a possible L-E contact, a class 2 fitting will
Dave(not Cockburn)
 15 May 2013 05:55 PM
At the luminaire, yes - from a circuit fault, no - IMO thats why BS 771 looks at the circuit of the location - not the luminaire, accessory, appliance etc.
A DI luminare doesn't create a DI system
 15 May 2013 07:14 PM
dg66
So if we get a fault on the circuit, what dangers will occur that wouldnt if any other non RCD circuit in the installation had a fault?
Dave(not Cockburn)
 15 May 2013 07:49 PM
Well any direct or indirect contact resulting from the failure of basic protection or fault protection or occuring from the carelesness of users.
So we may apply any of the measures in sections 411 to 414, but the RCD is still required as a backstop - ie it's for Additional Protection
 15 May 2013 09:44 PM
That, Mr OMS, is a fantastic summary of the requirements.
 15 May 2013 10:41 PM
John Peckham
I would agree with OMS in that it is Additional Protection and as it says on the tin it is Additional to other measureless of protection. Generally I would suggest it is easier to comply with the regulations than not to, Rectum Protectum. Just put an RCD fused connection unit over the entrance door and supply the lighting from that, as suggested by Stu above.
John Peckham
 15 May 2013 10:59 PM
dg66
whilst i agree an RCD will protect against the scenarios you mention, IMO additional protection is not required for these reasons, if that were the case every circuit regardless of location would require RCD protection for the scenarios you mention, i dont believe the regs cover carelessness by users, i've never seen this mentioned in the regs and as for direct contact ,i cant see this occuring in the location unless someone takes the fitting to bits and pokes their fingers where they dont belong, and indirect contact, well as its class 2 i dont see that as a problem (contact with a part thats become live due to a fault)
Dave(not Cockburn)
 16 May 2013 09:44 AM
Odd that 701.411.3.3 isn't numbered 701.415.1.something then?