Topic Title: New cu causing headache
Created On: 23 April 2013 06:08 PM
1 2 3 4 5 Next Last unread
jamesrussell
been on few weeks ago re rcd tripping when current drawn client has sold property and is reluctant for me to start pulling house to bits to find crossed neutral etc
I temporally put the sockets on the non rcd side of new board all other circuits protected
how will this reflect on me when he sells the house
 23 April 2013 06:28 PM
michaelbrett
What does your Elelectrical Installation Certificate state and has this been passed to the purchaser ?
Just been through this with a customer who purchased a house and all sorts of electrical issues - certificate does not reflect what has been done.
Customers solicitor now in 'discussion' with the vendor.
Mike
 23 April 2013 07:02 PM
jamesrussell
I installed and tested the cu about 8 weeks ago and everything seemed fine.
The client reckoned she came in after me and the decorator and all was fine.
however when they came in the other week to finish cleaning that's when the fridge freezer or the hoover tripped the rcd.
So when I did the cert it was ok what do I do?
 23 April 2013 07:03 PM
alanblaby
Why on earth did you energise socket outlets without RCD protection?
If anyone has a shock from an appliance you will be liable. You are liable now, you havent followed the regs, and cannot justify the reason for doing so.
I know many people do it occasionally, but generally as an overnight fix to keep the power on, never for more than a couple of days.
Get back and fix it.
jamesrussell
 23 April 2013 07:07 PM
jamesrussell
tell me why they would get more of a shock now than they would have done 2 months ago when it had fuse wire
 23 April 2013 07:13 PM
michaelbrett
James
You have carried out changes to the means of protection.
Unfortunetly, you were the last person to 'touch it'. So, if someone gets 'zapped', paperwork will probably get checked and well, you know the rest........
Did you do a full inspection prior to changing the CU? Did you document the data?
Did the client ever fully energise the installation prior to sale? Did it ever work with appliances plugged in?
Mike
 23 April 2013 07:17 PM
sparkiemike
It may have been unsafe then and it may be unsafe now - we don't know and it sounds like you don't because you don't know what the problem is?
Your problem is that you have "temporally put the sockets on the non rcd side of new board", are you saying you did this after you carried out your testing and issued a cert ?
I certainly would not have done that until I knew what the problem was. Was the client aware that you left the installation potentially unsafe?
 23 April 2013 07:29 PM
ady1
Hi James
What was supposed to be on 'the non RCD side' ?
Ady
Resistance is futile.
 23 April 2013 07:38 PM
perspicacious
"What was supposed to be on 'the non RCD side' ?"
BOD
 23 April 2013 07:45 PM
dg66
Originally posted by: ady1
Hi James
Ady
There can be a number of things not on an RCD, on my CU i,ve got
dual RCDs and two circuits without RCD protection. Four FCUs on one circuit to supply freezers a fridge and a tumble dryer and the cooker on another circuit, all compliant with BS 7671
Dave(not Cockburn)
 23 April 2013 07:49 PM
SKElectrical
Why not, the installation has likely been without RCD for 30+ years.
You are not liable, assuming your work isn't the cause of the fault.
If you agreed with customer to upgrade C/U with additional protection by means of RCDs, then you will have to either reimburse or find the fault (at an extra cost,, unless you specifically told cust you would upgrade C/U to current standards)
Originally posted by: michaelbrett
You have carried out changes to the means of protection (of the socket circuit)
No he hasn't.
 23 April 2013 07:50 PM
perspicacious
"all compliant with BS 7671"
Which edition?
BOD
 23 April 2013 08:01 PM
Jaymack
Head for the hills!
 23 April 2013 08:02 PM
WiredScience
Get the decorator back to find the trapped neutral where he/she has dropped and replaced the sockets?
 23 April 2013 08:13 PM
davezawadi
More kindly you have to consider:
If the cert you did is complete, accurate and reflects the exact installation meaning everything is fully tested, you have simply made an undocumented change to an installation as part of a repair process, which should be notified to the new owner as a work in progress, requesting access to complete the job (no charge to the new owner!!).
If the testing or cert are in any way "dubious" you have a problem and should notify the new owner that the entire installation will be tested, repaired and properly certified at no charge. If they agree (they probably will) you got off lightly.
Should you have a history of this kind of work, I suggest that Colombia might be better than France!
David
BSc CEng MIET
 23 April 2013 08:15 PM
jamesrussell
taking up gardening
 23 April 2013 08:32 PM
davezawadi
You need to sort this out first!
David
BSc CEng MIET
 23 April 2013 08:45 PM
dg66
Which edition?
BOD
17TH 2008 AMD1
Dave(not Cockburn)
 23 April 2013 10:18 PM
The fact that you have posted this suggests that you want to sort it out. So, do a Dave suggests, notify the new owners/occupants that there is an outstanding problem and that you need access to complete the remedial works. Re-certify the work as required and learn from the experience. The problem isn't that an rcd is tripping, that's doing its job, it's that the circuits has been fitted to a non-rcd protected circuit. The fault might be on an appliance not the circuit. Or maybe the circuit has changed since you tested it. Don't panic, get back and check the circuit and deal with the problem.