Hi all,
Customer complains they have been getting shocks from the sink and the dishwasher so I went to look.
Poor condition kitchen exemplified by a rotten and sagging work top behind the sink and drainer. Obviously a lot of moisture getting behind the units. Can see lots of copper underneath the plinth all green and grotty. Evidence of damp I think. Circuit is protected by 30A fuse wire and theres no RCD.
I measured 70V between the sink and the dishwasher. When I turned off the switched fuse to the dishwasher the voltage disappeared and remained near zero when I measured the pd between the sink and cooker circuit cpc and kitchen ring cpc. I didn't think to check if the sink was bonded but if isn't I'm not sure bonding would be the right thing top do because surely the voltage shouldn't be there in the first place.
I couldn't get the dishwasher out to check the outlet connections so have arranged for the customer to do so. In the meantime I have isolated the dishwasher from the supply and put up a warning notice on the switched fuse. I decided that in all probability the problem is damp or a loose cpc connection in the outlet connector. But if it is neither of these things, should I recommend they get someone look at the dishwasher or just bond the sink?
Simon
 11 April 2013 03:24 PM
bartonp
You could get ~70-80v just from an appliance 'floating' up due to filter capacitors on the mains. Need to know if there is any 'oomph' behind it... (tech term)
 11 April 2013 04:16 PM
tattyinengland
The only way to come to decision of any sort is to check the circuit:
R1+R2
IR
Visual inspection of the cable (Where ever possible including inside the switch fuse(s) and sockets)
Ze
Zdb
Zs
Make a decision.
I'd certainly recommend an RCD at the very least even if the circuit was seemingly perfectly fine, with the full knowledge that they're likely to go for it as they want to stop getting shocks and this might be caused by damp in an area you cannot see and may pass the tests on the day you do the tests if it is fairly dry - the dryer having been off for a while.
 11 April 2013 04:28 PM
But presumably the dishwasher is class 1 - so should be earthed rather than floating.
Sounds like a broken c.p.c. either inside the dishwasher, its flex, or fixed wiring.
Classic situation where metal pipework/earthed bonding carries dangers not present with all-insulated plumbing (although there'll always be a danger to another earthed class 1 appliance).
 11 April 2013 05:14 PM
Jaymack
What is the wiring type? VRI cables in conduit?.
 11 April 2013 05:37 PM
SKElectrical
Check earth at source, 'Main' earth.
It's no good saying you cant get behind the d/washer. All you've done is left it guessing and you need to get behind it at some point. You have to charge high and inform there may be surface d├ęcor to be repaired. Otherwise you end up discussing it and thinking about it without getting anywhere.
I would check other outlets' voltages L-N (or Ze). If they are okay then suggests fault with outlet behind washer.
Get some gloves and pull it out. If they don't want you to do that then wish them well.
Nasty job.
 11 April 2013 05:38 PM
esspeegee
PVC T&E. The spur that isolates the dishwasher is in the kitchen ring final and has a Zs of 0.54.
 11 April 2013 05:40 PM
I think Andy has the answer to this one, the dishwasher is not being earthed, most likely poor earth connection in the fcu i'd say,
 11 April 2013 05:43 PM
Zs 0.54
Sounds like the fcu has an earth then so probably broken earth connection inside the machine. Do a continuity test between the machine frame and the point where the earth connects to the fcu.
 11 April 2013 07:05 PM
tillie
Hi esspeegee , can you not test the casng of the dishwasher to confirm if it is earthed.
 11 April 2013 07:25 PM
mikejumper
To feel a voltage on the sink or dishwasher my guess is it's possibly more than just damp; you may have water resting across terminals or a JB.
 11 April 2013 11:31 PM
I agree. It is probably a lack of an earth connection to the dishwasher. Most of these devices have surge suppression on the incoming mains, which will result in the case sitting about half mains potential if you disconnect the earth.
 12 April 2013 11:30 AM
mikejumper
To have a voltage appear on the diswasher chassis unless it's earthed seems an odd design.
How good does the earth have to be?
Wouldn't a high Zs TT earth act as another potential divider across the suppression network?
 12 April 2013 05:05 PM
Nothing odd about it Mike, most class 1 appliances will have a small amount of earth leakage present especially where motors and surge/spike suppression capacitors are fitted,
 13 April 2013 04:21 PM
Zs
esspeegee, you have a more detailed pm from me.
I had similar last year and am seeing the property in my mind. Not a nice job and stressful as the anxious client watched over all the time. Dealing with this kind of thing on a rewireable is not easy.
In my case it was socket circuit not a dishwasher. Three days until I found the melted connector block under a floorboard where a spur had been added. They were hard-up, I did not want to leave them unsafe and it cost Zs dearly but was sorted.
So, I advise caution, the screwdriver in the lawn method and a concise discussion about your hourly fees right now.
Zs