My 'beloved' Fluke 1652 as developed yet another expensive looking fault. Ze and PEFC working ok but as soon as I toggle to do a L-N loop test ie PSC I get greater than 10kA. I've tried it on different installations, at different points in the installation always greater than 10kA and have tried setting the max reading to measure up to 50kA and it then tells me the PFC>50kA. Anyone had similar problems. I've found Fluke very cagey to deal with in the past. Last time they charged me £250 to repair a different fault and when I asked them for an explanation of what was wrong they told me it was their policy not to share that information. I tried adopting that same policy myself with a client recently following a fault finding call out and he told me to go and xxxx myself...weird?
Any help or pointers gratefully received.
Thanks
4.5 day wonder...had to start somewhere
 31 March 2013 09:27 AM
DR2366
You are zeroing your leads first aren't you?
 31 March 2013 09:34 AM
leckie
For a pfc test??
 31 March 2013 11:10 AM
PatHammond
For a Zs/Ze test with a Fluke you are supposed to zero the leads and this test will give you the PEFC and then you toggle to the L-N loop test with the leads still in situ (and still zeroed) and the LN loop will give you the PSC which in my case is always greater the 10kA
 31 March 2013 11:31 AM
leckie
I've got a meggar, never read about zeroing leads apart from continuity tests. Is this exclusive to Fluke?
 31 March 2013 12:23 PM
Zs
Pat, I agree that repairs are expensive. I once had a problem with mine, which I can't remember now, and was quoted over £200 for a repair. So I put it in for calibration at £80 and it came back fixed. That was Martindale in Watford.
That's a bit of a gamble but might help you?
The other thing to bear in mind is that a repaired item will come back with a fresh calibration certificate so if yours is going to be due soon it might sweeten the pill of the repair costs.
Zs
 31 March 2013 04:12 PM
hifly
Zs
when mine was repaired last year fluke wanted another £65, on top of the £250 repair cost for calibration, they did not tell me about this so it came back uncalibrated so i would of also had shipping costs.
it was also away for 3 weeks as it got overlooked.
Plus you only get a 3 month warranty on repairs.
I must say i am not impressed with their service.
mine currently has an intermittent fault where it see's a voltage that's not there so won't do the test, turning off then on seems to fix it until the next time.
Vince
"If you try and take a cat apart to see how it works, the first thing you have on your hands is a non-working cat."
http://www.ruttslanecider.co.uk/products
 31 March 2013 08:11 PM
sparkiemike
I can confirm it is a Fluke function, you connect all 3 leads, they supply a "zero adapter" and press the zero button. Like the Megger my Metrel does not have this function.
 31 March 2013 09:28 PM
slittle
All the more reason for me loving my megger then
I don't want to open an old debate but the industry has always "meggered" an insulation fault, never "fluked" one..... probably tells you fluke owners something.
Stu
 31 March 2013 10:03 PM
PatHammond
that age old dual
Fluke v Megger
Apple v Microsoft
Brown sauce v Tomato sauce
Ali v Frazier
N Korea v the rest of the world
Thanks for all your help everyone
 01 April 2013 11:01 AM
dg66
just do the PEFC test on L-N the instrument cant differentiate between N and E.