Topic Title: Load schedule for a delta connected motor
Created On: 28 March 2013 09:25 PM
MAXMIRA
Hi all,
Can anyone help me I have been given a load schedule for a 35kw delta connected motor. The load schedule shows the 35kw spread across the three phases I.e. 11.66kw per phase. I think this is incorrect as I would put it as 35kw per phase. Can anyone tell me which is the correct method and possibly back it up with some maths. Your help would be much appreciated.
Maxmira
 28 March 2013 09:29 PM
I'd take it as 35 kw spread across the phases.
It's been too longer week to do the maths for me, I'll let someone else have a crack at it.
 28 March 2013 10:07 PM
chunk522
It wouldnt be 35kw per phase, As Stu said you spread it across the 3 phase If memory serves me the calc is
Power / sqr3 x v x PF
Its a big motor though that is are you sure its not 3.5kw
 28 March 2013 10:40 PM
I've got 40kw floating pumps, it's not that big but it wouldn't start dol
 28 March 2013 10:54 PM
chunk522
LOL agreed
 29 March 2013 08:28 AM
Jaymack
I've got 40kw floating pumps, it's not that big but it wouldn't start dol [IMG][/IMG]
LOL agreed
Check with the supplier if you can't assess this yourself. A 40kW DOL motor is not a lot at 400V, but it depends on the capacity and protection of the supply to start such a motor, whilst maintaining an adequate starting torque and without an excessive voltage drop on the particular motor ...... and the whole installation. A maximum of 160 to 200kW DOL, is common in industry before using a higher voltage; but then they're usually designed for a stiffer supply.
 29 March 2013 08:48 AM
Jaymack
The motor input power = 1.73 × Volts (Line) × Amps (Line) × P.F.
The motor output power is the nameplate power = ditto ................ × Efficiency.
 29 March 2013 04:44 PM
LOL agreed
Perhaps I should have added "on a 100 amp supply, 600 metres from the cutout it doesn't want to start DOL".... We've got several star delta and three new ones on softstarts
 29 March 2013 10:57 PM
Vidas