Topic Title: How to derive three phase current for an isolation transformer Topic Summary: Created On: 22 March 2013 07:31 PM Status: Post and Reply |
Linear : Threading : Single : Branch |
Search Topic |
Topic Tools
|
|
|
|
|
Hi,
I wonder if any one can cast a light on which method should be used when calculating the required kva for a transformer. There are two school of thoughts: 1 - Use the highest phase current to determine the kVA 2 - Use the Average current of the three phases to deduce the kVA With the ever increasing cost of copper and decreasing amount of money being spent on asset option two is appealing, but does it meet regulatory requirements??? - Please help |
|
|
|
|
|
|
|
|
For a three phase transformer, use the highest phase current to calculate kVA for the most heavily loaded winding, then multiply this value by three. Finally, choose the next kVA size higher (as I doubt you are getting a device specially wound).
Regards, Alan. |
|
|
|
|