Topic Title: PME, Hi Ze, Impedance, Tx's
Topic Summary: Recomended reading?
Created On: 21 March 2013 07:23 AM
Status: Post and Reply
Linear : Threading : Single : Branch
Search Topic Search Topic
Topic Tools Topic Tools
View similar topics View similar topics
View topic in raw text format. Print this topic.
 21 March 2013 07:23 AM
User is offline View Users Profile Print this message



SherlockOhms

Posts: 322
Joined: 05 April 2011

Chaps,

Each time I read a thread on high Ze readings, PME, proximity to transformers and supply impedances etc I do begin to glaze over and things go foggy around the edges.

So, could sombody suggest some appropriate reading on all things related to the dark side of the cutout?

Many thanks,

S.
 21 March 2013 08:31 AM
User is offline View Users Profile Print this message


Avatar for Parsley.
Parsley

Posts: 1023
Joined: 04 November 2004

The IET electrical installation design guide to calculations and CIBSE guide K are both useful.

Regards
 21 March 2013 10:19 PM
User is offline View Users Profile Print this message


Avatar for UKPN.
UKPN

Posts: 514
Joined: 17 January 2012

capacity up to 100amps 230V single phase 0.38ohm
capacity up to 200amps/phase 400V 3 phase 0.38ohm

capacity from 200amps to 300amps/phase 400V 3 phase 0.20ohm
capacity exceeding 300 amps/phase 400v 3 phase 0.15ohms

higher values could apply to customers fed from small capacity pole mounted tx and/or long lengths of low voltage overhead overhead lines

Regards