When testing for earth leakage on an appliance using a leakage tester, does it matter if the jaws of the tester are over all three cables(if an earth cable is present) or should it only be around the live and neutral?
Also what is an acceptable leakage for an appliance say a vaccume cleaner? Thanks |
|
|
|
|
|
|
|
|
If testing for earth leakage you only really want the clamp meter on the earth cable,
Dave. |
|
|
|
|
|
|
|
|
Clamp the live and neutral with a good high resolution clamp meter - if you get any current measured that's the leakage as live in and neutral out will cancel any other load current
Dave - measuring the earth conductor assumes the leakage current is flowing through it - it could just as easily be going down a gas pipe Regards OMS ------------------------- Failure is always an option |
|
|
|
|
|
|
|
|
Agreed OMS but as the OP is testing appliances (vacuum cleaner he said) he only needs to know if anything's going down it's earth conductor, different for an installation test of course,
Dave. |
|
|
|
|
|
|
|
|
Also what is an acceptable leakage for an appliance say a vaccume cleaner? Thanks Take a look at CoP for In-service Inspection and Testing of Electrical Equipment 4th Edition page 96. You should also read page 95. Regards Mike |
|
|
|
|
|
|
|
|
Good point Dave - probably not credible that the vacuum has another means of earthing other than the CPC -
Although I'm sure we could construct a case where a class 1 hoover was situated on an earthed steel flooring system just to be awkward - in the tradition of the forum of course - regards OMS ------------------------- Failure is always an option |
|
|
|
|
|
|
|
|
Maximum for a class 1 vacuum cleaner is 0.75mA. Might be safer and easier to borrow a dedicated PAT instrument and run the appliance through it. Can a clamp type meter even measure that low? (I don't know)
|
|
|
|
|
|
|
|
|
I was "playing" with one the other day that has a resolution of 0.001mA
regards OMS ------------------------- Failure is always an option |
|
|
|
|
|
|
|
|
I was "playing" with one the other day that has a resolution of 0.001mA regards OMS I use a vacuum cleaner for cleaning the carpet........ Table 15.3 plus notes legh ------------------------- Why do we need Vernier Calipers when we have container ships? http://www.leghrichardson.co.uk "Science has overcome time and space. Well, Harvey has overcome not only time and space - but any objections." |
|
|
|
|
|
|
|
|
When testing for earth leakage on an appliance using a leakage tester, does it matter if the jaws of the tester are over all three cables(if an earth cable is present) or should it only be around the live and neutral? Thanks You could make yourself up a test lead by cutting off around 500mm of flex, slice open the outer sheath carefully about half way along and pull out a loop of earth conductor, then tape the sheath back up. Put a plug on one end and a trailing socket on the other end and you have the means to test individual appliances with a suitable clamp meter. |
|
|
|
|
|
|
|
|
I was "playing" with one the other day that has a resolution of 0.001mA That sounds useful - makes ours look like a toy at minimum 10mA. |
|
|
|
|
|
|
|
|
This short video from the Learning Lounge may be of use:
http://www.youtube.com/watch?v=5hL13UjRSoY It shows the modifed extension lead as mentioned by 'mikejumper' above. I think someone may have posted this video link on here before? ------------------------- M.I.E.T - Forfeited this due to The I.E.T's ridiculous membership rules! |
|
|
|
|
|
|
|
|
This short video from the Learning Lounge may be of use: http://www.youtube.com/watch?v=5hL13UjRSoY It shows the modifed extension lead as mentioned by 'mikejumper' above. I think someone may have posted this video link on here before? Oh dear! What is that guy trying to show with the class 2 equipment |
|
|
|
|
|
|
|
|
This short video from the Learning Lounge may be of use: ">http://www.youtube.com/watch?v...RSoY It shows the modifed extension lead as mentioned by 'mikejumper' above. I think someone may have posted this video link on here before? Oh dear! What is that guy trying to show with the class 2 equipment Lol, Why didn't he just clamp the two core cable? The difference between the phase and neutral would indicate the leakage.....would somebody then like to give an example of what type of appliance might cause this residual current? Legh ------------------------- Why do we need Vernier Calipers when we have container ships? http://www.leghrichardson.co.uk "Science has overcome time and space. Well, Harvey has overcome not only time and space - but any objections." |
|
|
|
|
|
|
|
|
I'm surprised at his 2mA 'blip' in the reading for the PS3. He seems to have the PS3 still connected to the TV which is plugged in somewhere else and has it's own earth. Presuming the PS3 has the mains earth connected to the data earth then he has 2 possible earth paths, only one that he's metering, and 2 sources of leakage, the TV and the PS3.
I doubt he would get that very precise 3.09mA if he just plugged all the appliances into the lead and measured the total, I suspect less than half that. |
|
|
|
|
|