Topic Title: External stair case Lightning or Bonding?
Created On: 19 March 2013 10:18 AM
irnbru
I have a new external steel stair case 5 floors high being erected onto an existing building. The building itself is 6 floors high with very old lightning protection i.e. untested in decades. Do I bond this stair to the MET or consider seperate lightning protection or connect to existing lightning protection and test or ???
 19 March 2013 11:22 AM
Avatar for OMS.
Does it introduce a potential into the building - I suspect not - so not required to have main equipotential bonding
Is it more than likley a self protecting structure in terms of lightning protection - I would say yes - it's location may also put it into the protection zone offered by a rolling sphere analysis or angle of protection method calculation which would probably confirm the self protection and that it's not a risk structure given its relative location to the building
It will need bonding to existing LPS to prevent side flashing and may need a connection to an electrode if you cannot determine connectivity to any rebar etc in the foundation pad
Existing LPS should be made compliant - at least in the area of the stairway
There should be a single point of common bonding from the Building MET to the LPS system
How far your design needs to go with all that is probably a matter of your appointment document but the technical content is generally as above.
Failure is always an option
 19 March 2013 11:24 AM
GB
If memory serves then if your existing lightning protection is up to standard it will generally (30 deg coverage from roof edge) cover the external staircase, I would get in a lightning protection specialist to advise on existing system and whether a link to the staircase is required.
 21 March 2013 06:07 PM
Avatar for Legh.
Legh
Will the external stairs have any lights on them ?
Legh
 16 May 2013 06:07 PM
irnbru
Just an update really. The stairs had no electriclal equipment installed on it. The LPS guys just connect it to existing LPS.