Hi guys
I have a quote to do in a bath room.where the customer has a fitted cupboard, in which they want an Ironing board of all things.
the Ironing store is over 600mm from zone 2.
I intend to shorten the Iron flex to a length it will not reach any thing,have it as a fixed load. install sup bonding to all services.
power circuit is RCD protected and I intend to RCD lighting so really supp bonding is over the top but due to the unusual situation bibs and braces.
any comments
 18 March 2013 01:19 PM
beaver74
also they would like the fixed load swithed in the cupboard
 18 March 2013 01:46 PM
OMS
any comments
Yes - where will the client actually do the ironing ? - and how is that any different from plugging into a socket on the landing (for example) given the cupboard is outside of zones anyway.
Regards
OMS
Let the wind blow you, across a big floor.
 18 March 2013 01:50 PM
MrP
Not sure without looking in the book the distance of Zones but if you look in section 6 bobs your uncle
I think the lady of the house will be after you if you shorten the flex re switch again look what sec 6 says
If I had to make an on the spot decision I would say OK
If it's Rcd why bother sup bonding
Was there a James Bond flim where JB throw an iron into the bath and the Chinese bloke with the bald head got zapped
MrP rapping for the day, today is the year 5 since a shovel was put in the ground with 9,000 men on site and not one room finished you couldnt make it up
 18 March 2013 01:57 PM
beaver74
Originally posted by: OMS
any comments
Regards
OMS
there is room to get the Iron out as it is rather a large room which is why we have the room between cupboard an shower bath
 18 March 2013 02:00 PM
beaver74
Part 7 bath rooms has nothing about out side zone 2. which it used to
 18 March 2013 02:19 PM
daveparry1
That was when outside zone 2 could be whithin zone 3? Now that zone 3 doesn't exist they'd have no reason to mention it!
Dave.
 18 March 2013 02:36 PM
AJJewsbury
The last sentence of 701.512.3 does in my copy - 2.4m outside zone 2 to be precise.
 18 March 2013 02:52 PM
beaver74
well spoted