Topic Title: fixed load in a bath room
Topic Summary:
Created On: 18 March 2013 01:16 PM
Status: Post and Reply
Linear : Threading : Single : Branch
Search Topic Search Topic
Topic Tools Topic Tools
View similar topics View similar topics
View topic in raw text format. Print this topic.
 18 March 2013 01:16 PM
User is offline View Users Profile Print this message



beaver74

Posts: 361
Joined: 07 February 2007

Hi guys

I have a quote to do in a bath room.where the customer has a fitted cupboard, in which they want an Ironing board of all things.

the Ironing store is over 600mm from zone 2.

I intend to shorten the Iron flex to a length it will not reach any thing,have it as a fixed load. install sup bonding to all services.
power circuit is RCD protected and I intend to RCD lighting so really supp bonding is over the top but due to the unusual situation bibs and braces.

any comments
 18 March 2013 01:19 PM
User is offline View Users Profile Print this message



beaver74

Posts: 361
Joined: 07 February 2007

also they would like the fixed load swithed in the cupboard
 18 March 2013 01:46 PM
User is offline View Users Profile Print this message


Avatar for OMS.
OMS

Posts: 19655
Joined: 23 March 2004

any comments


Yes - where will the client actually do the ironing ? - and how is that any different from plugging into a socket on the landing (for example) given the cupboard is outside of zones anyway.

Regards

OMS

-------------------------
Failure is always an option
 18 March 2013 01:50 PM
User is offline View Users Profile Print this message



MrP

Posts: 837
Joined: 24 March 2006

Not sure without looking in the book the distance of Zones but if you look in section 6 bobs your uncle
I think the lady of the house will be after you if you shorten the flex re switch again look what sec 6 says
If I had to make an on the spot decision I would say OK
If it's Rcd why bother sup bonding
Was there a James Bond flim where JB throw an iron into the bath and the Chinese bloke with the bald head got zapped

MrP rapping for the day, today is the year 5 since a shovel was put in the ground with 9,000 men on site and not one room finished you couldnt make it up
 18 March 2013 01:57 PM
User is offline View Users Profile Print this message



beaver74

Posts: 361
Joined: 07 February 2007

Originally posted by: OMS

any comments




Yes - where will the client actually do the ironing ? - and how is that any different from plugging into a socket on the landing (for example) given the cupboard is outside of zones anyway.



Regards



OMS


there is room to get the Iron out as it is rather a large room which is why we have the room between cupboard an shower bath
 18 March 2013 02:00 PM
User is offline View Users Profile Print this message



beaver74

Posts: 361
Joined: 07 February 2007

Originally posted by: MrP

Not sure without looking in the book the distance of Zones but if you look in section 6 bobs your uncle

I think the lady of the house will be after you if you shorten the flex re switch again look what sec 6 says

If I had to make an on the spot decision I would say OK

If it's Rcd why bother sup bonding

Was there a James Bond flim where JB throw an iron into the bath and the Chinese bloke with the bald head got zapped



MrP rapping for the day, today is the year 5 since a shovel was put in the ground with 9,000 men on site and not one room finished you couldnt make it up


Part 7 bath rooms has nothing about out side zone 2. which it used to
 18 March 2013 02:19 PM
User is offline View Users Profile Print this message



daveparry1

Posts: 6200
Joined: 04 July 2007

That was when outside zone 2 could be whithin zone 3? Now that zone 3 doesn't exist they'd have no reason to mention it!

Dave.
 18 March 2013 02:36 PM
User is offline View Users Profile Print this message



AJJewsbury

Posts: 11424
Joined: 13 August 2003

Part 7 bath rooms has nothing about out side zone 2

The last sentence of 701.512.3 does in my copy - 2.4m outside zone 2 to be precise.
- Andy.
 18 March 2013 02:52 PM
User is offline View Users Profile Print this message



beaver74

Posts: 361
Joined: 07 February 2007

Originally posted by: AJJewsbury

Part 7 bath rooms has nothing about out side zone 2


The last sentence of 701.512.3 does in my copy - 2.4m outside zone 2 to be precise.

- Andy.


well spoted