Topic Title: No Lighting cpc's
Created On: 17 March 2013 10:24 PM
alpelec
I recently replaced a consumer unit, upgraded bonding, replaced metal light fittings on a house with no lighting cpc's. When filling in the Electrical installation certificate there is a check box under 'fault protection' for 'presence of circuit protective conductors'. On the NICEIC ones you can only put a tick or N/A. Since neither is applicable does anyone know what you would do here?
 17 March 2013 10:39 PM
OldSparky
that is true, no lim on an installation cert..
i do an eicr
 17 March 2013 10:53 PM
Put n/a in the R1+R2 and Zs boxes on the lighting circuit line of the test results page and a note in the "comments on existing installation" box. Put the appropriate label on the c/unit, that's as much as you need to do for a c/unit change,
 17 March 2013 11:22 PM
alpelec
Thanks Dave, I've done that in the test results but what about the schedule tick box?
 18 March 2013 08:08 AM
Tick that as ok because your comments will cover that one circuit that's not earthed,
 18 March 2013 10:05 AM
Basic point here is that you're only certifying the work you've just done - as you've not installed the circuits lacking c.p.c.s you're not certifying them - just your work to re-connect them and sufficient proof that you've not made any non-compliant parts of the overall installation less safe than they previously were. As Dave says, the "comments on existing installation" box is the place to explain any oddities.