Does anyone have any data on a 1000A ACB Type B517 such as the fault current rating?
John Peckham
http://www.astutetechnicalservices.co.uk/
 06 March 2013 07:31 PM
OMS
Not a reference I recognise John - what range is it from.
Generally speaking all Schneider (and previous MG) ACB's were minimum of 50kA fault rating.
Regards
OMS
Let the wind blow you, across a big floor.
 06 March 2013 07:37 PM
John Peckham
I will email you a picture.
John Peckham
 06 March 2013 08:02 PM
OMS
OK - not one I know well John, I think we had a few on a couple of hospital sites - I see if I can find some legacy data on it.
regards
OMS
 06 March 2013 08:27 PM
robuck
John
You could try Schneider Electric technical help in the morning
Regards
Rod
 06 March 2013 09:03 PM
dbullard
I tried Schnieder technical about an old Vigi unit ....... anything older than 10 minutes they have no details ....
Regards
Daren
..... Dont pee in my pocket and tell me its raining ......
www.quest-electrical-sw.co.uk
 07 March 2013 09:50 PM
UKPN
50ka min is correct, but 3 levels of breaking capacity give you 70 and 150. (for 800, 1000 and 1250)
Regards
 07 March 2013 09:56 PM
dlane
Our old MPACT units were 50kA max.
Our Schneider Masterpact NT ACBs started at 50kA and went up to 105kA.
If you can post the manufacturer and type, I could look through my PTW database to see if there is any data in there.