Topic Title: Parrallel Supplies
Topic Summary: Number of parallel conductors
Created On: 06 March 2013 01:39 PM
carllangwood
When sizing parrallel supply cables, is it a requirement to install three conductors to allow for failure of one, therefore the remaining two conductors are capable of maintaining the full load.
 06 March 2013 01:48 PM
Avatar for OMS.
Not usually, no - and it would be a very particular fault that open circuited a single conductor without influencing the other as they should be approx the same length and run generally in close proximity.
The choice of grouping ie 2 x, trefoill, 4 x or 5 x is generally a function of load versus conductor size/route and need for "equal" current sharing by conductors of a group.
Failure is always an option