 06 March 2013 01:39 PM
User is offline View Users Profile Print this message



carllangwood

Posts: 8
Joined: 08 February 2012

When sizing parrallel supply cables, is it a requirement to install three conductors to allow for failure of one, therefore the remaining two conductors are capable of maintaining the full load.
 06 March 2013 01:48 PM
User is offline View Users Profile Print this message


Avatar for OMS.
OMS

Posts: 18919
Joined: 23 March 2004

Originally posted by: carllangwood

When sizing parrallel supply cables, is it a requirement to install three conductors to allow for failure of one, therefore the remaining two conductors are capable of maintaining the full load.


Not usually, no - and it would be a very particular fault that open circuited a single conductor without influencing the other as they should be approx the same length and run generally in close proximity.

The choice of grouping ie 2 x, trefoill, 4 x or 5 x is generally a function of load versus conductor size/route and need for "equal" current sharing by conductors of a group.


Regards

OMS

-------------------------
Failure is always an option