Topic Title: tester problem Topic Summary: Created On: 04 March 2013 07:36 PM Status: Post and Reply |
Hi has anyone had this issue with their tester before ? when I test ze I get a good reading say 0.2 ohms. but when I test the zs of a circuit the reading is higher than it should be. if I know ze 0.2 and R1R2 is 0.2 . but ze may come out at 1 ohm and its not just this circuit. Then to see I tested at the load side of the rcd but all mcbs off and get 0.65 but ze is 0.2. its the same for both rcds on the board. faulty tester leads ???
read the mk rcd post a few below this one might shed a bit of light. In fact there are several related to testing through rcd's
Gary ------------------------- Specialised Subject. The Bleedin Obvious. John Cleese |
Whats the resolution on the non trip setting on your tester? It might be way off what you might think acceptable (i know, i had one like this, it got retired)
Whats the make and model? ------------------------- ---------------------------------------- Lack of planning on your part doesn't make it an emergency on mine.... Every man has to know his limitations- Dirty Harry |
just read the mk post. my board was mk also, seems they are a bit of a pain