Topic Title: Cooker cable capacity Topic Summary: Description in manual confusing- says mains in=3 x 2.5mm Created On: 23 February 2013 03:42 PM Status: Post and Reply |
Linear : Threading : Single : Branch |
Search Topic |
Topic Tools
|
|
|
|
|
Changing my integral double oven, I find new cooker terminals do not have clamps under "screw" heads, and finding it impossible to get good grip on cables.
Cooker spec says main in cable should be 3 x "2.5mm"- not quite sure what that means, apart from totalling 7.5mm; is a Baumatic double oven. My current 6mm cable is stranded not solid; if changed for solid I'd imagine still very difficult to retain cable under screw heads. Any suggestions valued? ------------------------- Gel__Big Brother is here |
|
|
|
|
|
|
|
|
I think they are referring to each conductor, ie L N E all of 2.5mm csa. If you can't make a satisfactory connection by splitting the cores of the 6mm and putting 3 cores on one side of the screw and 4 on the other use a cooker outlet plate or a junction box to convert the 6mm t/e into 2.5 mm flex. Are you sure those instructions are for single phase supplies? sometimes they give two sets of instructions, 2.5mm for 400v 3 phase supplies and 4mm for 230v single phase with link plates to be fitted in their terminal block,
Dave. |
|
|
|
|
|
|
|
|
Is there one live terminal or three? There could be the option to make a three phase electrical supply option, in which case there may be some little brass links packed some where, normally in the terminal box held in a moulded section of the box or in the terminals themselves, these links can be used to link three live terminals if that is what you have to allow a single phase connection.
Andy |
|
|
|
|
|
|
|
|
Thanks all; space under & around screw head in it's plastic shroud very limited.
It's a Euro spec oven I believe as allows for 230v single phase, or 400/230 2 phase via some bridging adjustments. I found T4 the recommened for Neutral would not tighten; therefore as the other N terminal 5, is bridged to it, ran N to 5. However, though upper oven works, fan oven below is dead. I'm wondering if it's because I didn't use one nominated, or perhaps because bridge plate on T4 can't be properly tightened. Tks, ------------------------- Gel__Big Brother is here |
|
|
|
|
|
|
|
|
If things don't tighten then get the suppliers to send you an item that is fit for purpose and ask them for some decent instructions.
I seem to recall that manufacturers are required to supply decent instructions in some bit of obscure consumer law. |
|
|
|
|
|
|
|
|
The instructions are decent as is adjacent wiring guide label on cooker; however, connecting cable strands to cooker is taken as red.
eg all terminal screws must be tightened securely. That would be easy, if it wasn't for the cable starnds!! ------------------------- Gel__Big Brother is here |
|
|
|
|
|
|
|
|
Sounds like it might be designed for a 2.5mm flex ?
what is its rating ? Gary ------------------------- Specialised Subject. The Bleedin Obvious. John Cleese |
|
|
|
|
|
|
|
|
Here we go:
Rated Voltage: 220-240 Vac 50 Hz Max Rated Inputs: 5.60 kW Mains Supply Lead 3 x 2.5 mm² (not supplied) ------------------------- Gel__Big Brother is here |
|
|
|
|
|
|
|
|
Here we go: Rated Voltage: 220-240 Vac 50 Hz Max Rated Inputs: 5.60 kW Mains Supply Lead 3 x 2.5 mm² (not supplied) Remove the screws crimp terminals on stranded cables place screw through terminal tighten up. Bingo ------------------------- Regards Martyn. Only a mediocre person is always at their best www.electrical contractors uk.com |
|
|
|
|
|
|
|
|
To me, that reads that the oven is intended to be wired using a 3-core 2.5mm cable. Without any further information, I would expect that to be 2.5mm heat-resistant flex.
So the problem is that you are trying to jam a 6mm cable into a terminal meant for 2.5mm. ------------------------- S P Barker BSc PhD MIET |
|
|
|
|
|
|
|
|
seems to be quite common these days, imported cookers requiring a non-standard ( well i don't carry 2.5mm 3core hr flex) flex or cable connection that would have cost them peanuts to have fitted in the overall cost of the cooker. I had to source some 6mm 5core flex a while back for a 3 phase cooker, an absolute pain in the backside and cost a fortune.
Gary ------------------------- Specialised Subject. The Bleedin Obvious. John Cleese |
|
|
|
|
|
|
|
|
As suggested 2.5mm cable seems to be the fix.
------------------------- Gel__Big Brother is here |
|
|
|
|
|