Topic Title: rcd failed?
Topic Summary: is this right?
Created On: 21 February 2013 09:01 PM
davettherave
hi at 1 x in rcd read 310ms at 1 x read 18ms
is this a fail?
 21 February 2013 09:07 PM
Read what you posted again. I assume your talking a 30mA rcd.
 21 February 2013 09:11 PM
davettherave
yes mate
 21 February 2013 09:15 PM
davettherave
just googled 300ms seems to be a fail
new rcd ?
 21 February 2013 09:31 PM
Did you have all loads disconnected?
 21 February 2013 10:16 PM
davettherave
i didnt test it just been asked to quote on someone elses ecr
they gave it a code 2 even though 18ms at 5 x
 22 February 2013 07:11 AM
alanblaby
If whoever tested it did it properly, then the results may be correct, and, if you now go and test it again, it may give acceptable results every time.
I'd guess at it not being tested for a long time, the Tester did it correctly and did half times and 1 times 30mA, and found it was sticking, by giving the 310mS result. Once it had tripped once, the results would then be acceptable, as the corrosion/sticking had been cleared.