ive just inspected some downlighters in a flat wired in flex and earths etc cut out as usual.

couldnt test zs

what code should i give this?
 21 February 2013 08:12 PM
User is online View Users Profile Print this message



daveparry1

Posts: 6102
Joined: 04 July 2007

Are the lamps class 1 or class 2 then?
 21 February 2013 08:25 PM
User is offline View Users Profile Print this message



davettherave

Posts: 38
Joined: 06 May 2012

gu 10 fittings not fire rated either
 21 February 2013 08:28 PM
User is online View Users Profile Print this message



daveparry1

Posts: 6102
Joined: 04 July 2007

But are they class 2 therefore not requiring an earth connection?
 21 February 2013 08:35 PM
User is offline View Users Profile Print this message



davettherave

Posts: 38
Joined: 06 May 2012

yes lets asume they are class 2.
 21 February 2013 08:36 PM
User is offline View Users Profile Print this message



davettherave

Posts: 38
Joined: 06 May 2012

or lets assume? quote to i replace them with a class 2 fitting!
 21 February 2013 09:43 PM
User is offline View Users Profile Print this message


Avatar for Martynduerden.
Martynduerden

Posts: 3211
Joined: 13 July 2008

Originally posted by: davettherave

ive just inspected some downlighters in a flat wired in flex and earths etc cut out as usual.

couldnt test zs

what code should i give this?


No issue with flex its permitted in the 17th.

Most down lights don't require an earth but the cables do. code 1.

-------------------------
Regards

Martyn.

Only a mediocre person is always at their best



www.electrical contractors uk.com
 21 February 2013 10:22 PM
User is offline View Users Profile Print this message



davettherave

Posts: 38
Joined: 06 May 2012

cant place label stating no cpc lighting circuit and code 3 then?
 21 February 2013 10:27 PM
User is offline View Users Profile Print this message



davettherave

Posts: 38
Joined: 06 May 2012

what about best practice guide 2 page 6 & 7?
 21 February 2013 10:37 PM
User is offline View Users Profile Print this message


Avatar for dickllewellyn.
dickllewellyn

Posts: 1150
Joined: 19 March 2010

If the fittings are class two, then no code in my book. Probably didn't have twin flex on the van, so,used three core and cut the cpc off.

-------------------------
Regards
Richard (Dick)

"Insert words of wisdom and/or witty pun here"
 21 February 2013 11:15 PM
User is offline View Users Profile Print this message


Avatar for Martynduerden.
Martynduerden

Posts: 3211
Joined: 13 July 2008

Originally posted by: davettherave

cant place label stating no cpc lighting circuit and code 3 then?


No. It has a floating cpc, which could actually be more dangerous than no cpc.

Like I say It's a code 1 for the cable being installed outside manufacturers spec, cpc not connected to the end of the circuit.

-------------------------
Regards

Martyn.

Only a mediocre person is always at their best



www.electrical contractors uk.com
 22 February 2013 07:07 AM
User is offline View Users Profile Print this message



Jaymack

Posts: 4586
Joined: 07 April 2004

Originally posted by: Martynduerden
Like I say It's a code 1 for the cable being installed outside manufacturers spec, cpc not connected to the end of the circuit.

The CPC if present on the feed cable to a class II fitting, and connected to the earth bar ensures that the cable is protected throughout it's length, and the means of obtaining Zs. Otherwise there is no code, but what code for the inspector here?.

Regards
 22 February 2013 07:14 AM
User is offline View Users Profile Print this message


Avatar for ebee.
ebee

Posts: 5666
Joined: 02 December 2004

Isn`t code 1 a tadd severe?

Why was flex a no no on fixed wiring until quite recently?

and what has changed since to make it now acceptable?

-------------------------
Regards,
Ebee (M I S P N)

Knotted cables cause Lumpy Lektrik
 22 February 2013 07:21 AM
User is offline View Users Profile Print this message


Avatar for dickllewellyn.
dickllewellyn

Posts: 1150
Joined: 19 March 2010

Originally posted by: ebee
and what has changed since to make it now acceptable?


Our European cousins use it!

-------------------------
Regards
Richard (Dick)

"Insert words of wisdom and/or witty pun here"
 22 February 2013 08:21 AM
User is offline View Users Profile Print this message



broadgage

Posts: 1265
Joined: 07 August 2007

A code 1 seems OTT, surely a code 1 is for immediate danger ?
What immediate danger is there in a class 2 fitting not being earthed ?

I grant that the CPC in the flex should be earthed, but would consider the ommision of such to be very low risk indeed as the flex is presumably out of reach and at little risk of damage.

Code 3 if any IMHO.
 22 February 2013 09:54 AM
User is offline View Users Profile Print this message


Avatar for Martynduerden.
Martynduerden

Posts: 3211
Joined: 13 July 2008

Originally posted by: broadgage

A code 1 seems OTT, surely a code 1 is for immediate danger ?

What immediate danger is there in a class 2 fitting not being earthed ?

I grant that the CPC in the flex should be earthed, but would consider the ommision of such to be very low risk indeed as the flex is presumably out of reach and at little risk of damage.

Code 3 if any IMHO.


I don't make the regs, an electrician may well get a shock from that section of unconnected cpc.

-------------------------
Regards

Martyn.

Only a mediocre person is always at their best



www.electrical contractors uk.com
 22 February 2013 10:10 AM
User is offline View Users Profile Print this message



AJJewsbury

Posts: 11269
Joined: 13 August 2003

an electrician may well get a shock from that section of unconnected cpc.

How would that work? Capacitive coupling producing >10mA?

Is it any more dangerous than the 'floating' strapper in a 2-way switching system when both switches are in the same position?

.. or a switch wire with the lamp removed?

- Andy.
 22 February 2013 11:47 AM
User is offline View Users Profile Print this message


Avatar for jsa986.
jsa986

Posts: 472
Joined: 08 February 2011

@Davethehrave why are you "assuming class two" have you not checked? You also state they are not fire rated but have not stated if they are ground floor or upstairs? plus fire rating is building regs not electrical, some advice rather than code may be sensible here

@ Mertyuereden, no one is saying you make the regs, the others are simply telling you no earth to class two fitting is hardly a code 1 (immediate danger) and I have to agree

-------------------------
www.icertifi.co.uk
Electrical & Gas Certificates on iPhone & iPad
 22 February 2013 12:30 PM
User is offline View Users Profile Print this message



MrP

Posts: 831
Joined: 24 March 2006

All points of utilisation should be earthed irrespective whether class 1or2 the thought behind if the class 2 fittings get changed to class 1 therefore non compliance.
Wiring method flexible cable no problem, interesting how final connection made if daisy chained getting two flexible cables into one terminal, fitting designed to accept two cables? Possibly non compliance.
What code ? does it matter as long as you have produced a report it's not a numbers game the codes are a guide to the report make your own numbers game up, call it a 5C that will get them thinking
it's a non compliance
MrP Going home in 6days
 22 February 2013 01:26 PM
User is offline View Users Profile Print this message



broadgage

Posts: 1265
Joined: 07 August 2007

I would agree that points of utilisation should be earthed, to allow for future changes. But I would also consider the absence of this earth to be a minor non-compliance IF class 2 fittings are used.

I would still say code 3, non compliant but not actually dangerous.

Just like an old lighting circuit with no CPC, but all plastic fittings.