IET logo
 
IET
Decrease font size
Increase font size
Topic Title: Loadstar rcbos
Topic Summary: Strange readings
Created On: 16 February 2013 06:46 PM
Status: Post and Reply
Linear : Threading : Single : Branch
Search Topic Search Topic
Topic Tools Topic Tools
View similar topics View similar topics
View topic in raw text format. Print this topic.
 16 February 2013 06:46 PM
User is offline View Users Profile Print this message



tillie

Posts: 719
Joined: 03 May 2006

Hi , I installed two radial circuits for a kitchen in a commercial premises.

I have installed each circuit on its own B20 Loadmaster Rcbo.

Tested the Rcbos Today and came across a problem with one of the Rcbos.

On 1x test it tests fine , but on the 5x test on 180 degrees it kept giving me >40. It tests fine on 0 degrees 7.9ms.

It will only test fine if I actually disconnect the load at the Rcbo 18.3ms.

Now I know that the Rcbo should be tested with the load disconnected but I have never had to physically disconnect the outgoing load from the Rcbo before, I would just make sure that all loads were disconnected from the circuit.

Is the Rcbo good or should I replace it.

Regards
 16 February 2013 07:42 PM
User is offline View Users Profile Print this message



daveparry1

Posts: 5271
Joined: 04 July 2007

If it tests ok off-load I wouldn't worry about it Tillie, that's the way we're told to do it!

Dave.