IET logo
 
IET
Decrease font size
Increase font size
Topic Title: Recording clearly 'wrong' test results?
Topic Summary:
Created On: 15 February 2013 08:53 PM
Status: Post and Reply
Linear : Threading : Single : Branch
1 2 Next Last unread
Search Topic Search Topic
Topic Tools Topic Tools
View similar topics View similar topics
View topic in raw text format. Print this topic.
 15 February 2013 08:53 PM
User is offline View Users Profile Print this message



alanblaby

Posts: 166
Joined: 09 March 2012

Doing an install today, MK dual RCD board, short radial in 2.5mm T+E, R1 + R2 is around 0.15ohms.
Zs, when using the meter is around 1.1 ohms.
Ze fine at around 0.27.

We know the meter can record readings through the CB and RCD, so gives a slightly false reading, but this was a lot higher than the true figure.

Similar readings were taken on other circuits too - typical 0.75 to 1.5 ohms higher than the calculated figure would be.

So, on the EIC, do I record the meter reading, or just calculate?
 15 February 2013 08:56 PM
User is offline View Users Profile Print this message


Avatar for slittle.
slittle

Posts: 3081
Joined: 22 November 2007

I would calculate and check the meter on the next job, if it's still suspect send it off for calibration/repair


Stu
 15 February 2013 09:04 PM
User is offline View Users Profile Print this message



daveparry1

Posts: 5272
Joined: 04 July 2007

Sounds like suspect connections when you were testing Zs,

Dave.
 15 February 2013 09:04 PM
User is offline View Users Profile Print this message


Avatar for sparkingchip.
sparkingchip

Posts: 5296
Joined: 18 January 2003

"We know the meter can record readings through the CB and RCD, so gives a slightly false reading, but this was a lot higher than the true figure."

Why is it not the true figure?
 15 February 2013 09:09 PM
User is offline View Users Profile Print this message



londonlec

Posts: 61
Joined: 29 November 2010

Ive had this recently with an MK dual board, I tested the incoming and outgoing sides of the RCD and found a 0.50 ohms difference (roughly).
 15 February 2013 09:18 PM
User is offline View Users Profile Print this message


Avatar for sparkingchip.
sparkingchip

Posts: 5296
Joined: 18 January 2003

?
 15 February 2013 09:23 PM
User is offline View Users Profile Print this message



alanblaby

Posts: 166
Joined: 09 March 2012

Meter is fine, used everyday this week, came home, and tested a socket I use for the monthly check and it was 0.02 ohms out, which is quite acceptable.
It was tested on a brand new socket, then via the probes on a FCU on the same circuit this afternoon, both readings were virtually the same, and every circuit gave much higher readings than expected.

Sparkingchip - havent you come across this before? Maybe it is only certain meters that do it, this was Dilog 9083.
 15 February 2013 09:24 PM
User is offline View Users Profile Print this message



John Peckham

Posts: 6880
Joined: 23 April 2005

What meter did you use for the loop test?

-------------------------
John Peckham

http://www.astutetechnicalservices.co.uk/
 15 February 2013 09:35 PM
User is offline View Users Profile Print this message


Avatar for slittle.
slittle

Posts: 3081
Joined: 22 November 2007

I've seen it happen with my megger (not to that degree) if you ze on high current and zs on no trip (low current).

I have heard of some RCD's doing "strange" things to the zs readings but we've fitted MK boards and none of my guys have reported a problem so far.


Stu
 15 February 2013 09:49 PM
User is offline View Users Profile Print this message


Avatar for sparkingchip.
sparkingchip

Posts: 5296
Joined: 18 January 2003

So isn't the RCD part of the circuit?

Andy
 15 February 2013 09:52 PM
User is offline View Users Profile Print this message



John Peckham

Posts: 6880
Joined: 23 April 2005

Stu that was my thinking high current test vs low current test.

-------------------------
John Peckham

http://www.astutetechnicalservices.co.uk/
 15 February 2013 09:54 PM
User is offline View Users Profile Print this message


Avatar for slittle.
slittle

Posts: 3081
Joined: 22 November 2007

Yes of course, but as I said earlier if you high current pre rcd and low current after odd things appear to happen sometimes.



Stu
 16 February 2013 09:23 AM
User is offline View Users Profile Print this message



aligarjon

Posts: 2441
Joined: 09 September 2005

i rarely do zs tests anymore they are a waste of time with rcd's in circuit, i always calculate from Ze.

Gary

-------------------------
Specialised Subject. The Bleedin Obvious. John Cleese
 16 February 2013 09:38 AM
User is offline View Users Profile Print this message



daveparry1

Posts: 5272
Joined: 04 July 2007

That doesn't take into account parallel paths though Gary, (probably doesn't matter that much in practice though)

Dave.
 16 February 2013 06:20 PM
User is offline View Users Profile Print this message



tillie

Posts: 719
Joined: 03 May 2006

Hi , this week I installed four Electrak underfloor busbars.

Today I tested before energising.

I have a Zdb of 0.04 ohms and an R1 + R2 of 0.19 ohms at the furthest point on the Electrak , so I was expecting a reading of around 0.23 ohms.

Tested on low test because they are Rcd protected and got readings of 0.62.

I have no intention of recording that result because I know it is nonsense , so I intend to use the calculated value.

I also tried testing on high current mode and noticed that two of the Rcds did not trip and gave me readings that I expected.

Circuits all tested fine.

Are the Rcds not tripping when tested under the high current test something to worry about , I do not remember it happening to me before.

Rcd tests were also carried out and were all fine and well within limits.

Tester is a Megger 1552.

Regards
 16 February 2013 07:37 PM
User is offline View Users Profile Print this message



daveparry1

Posts: 5272
Joined: 04 July 2007

If you used a "grown up's tester" like a Fluke you wouldn't be getting these problems. The Fluke doesn't use a low current test to avoid tripping rcd's, it uses a very short time interval for the test instead!

Please take the reference to grown up tester as a joke but I have seen this problem here so often it makes me wonder why anyone uses the Megger mft?

Dave.
 17 February 2013 09:57 AM
User is offline View Users Profile Print this message



Jaymack

Posts: 4291
Joined: 07 April 2004

Originally posted by: daveparry1
That doesn't take into account parallel paths though Gary, (probably doesn't matter that much in practice though)

Au contraire, In general, a Zs measurement errs positively and proof of the pudding, if a supply is available! For belt and braces one could carry out both

A person with 2 watches never knows the correct time!

Regards

Edited: 17 February 2013 at 10:39 AM by Jaymack
 17 February 2013 03:05 PM
User is offline View Users Profile Print this message


Avatar for dbullard.
dbullard

Posts: 1165
Joined: 02 March 2006

Originally posted by: daveparry1

If you used a "grown up's tester" like a Fluke you wouldn't be getting these problems. The Fluke doesn't use a low current test to avoid tripping rcd's, it uses a very short time interval for the test instead!


Please take the reference to grown up tester as a joke but I have seen this problem here so often it makes me wonder why anyone uses the Megger mft?

..................................................................................................................

Dave I have 3 sets of Megger, 2 x sets of single and a MFT 1720. I am really p####d of with 1720, the lead sets are cr#p been back for repair twice and had a software upgrade ???? which makes it a 1552, my original set of Megger's are 15+ years old and just about to up to 17th edition standards, I regularly use these still as I know and trust the readings I have no faith in the MFT.

-------------------------
..... Dont pee in my pocket and tell me its raining ......


www.quest-electrical-sw.co.uk
 17 February 2013 08:52 PM
User is offline View Users Profile Print this message


Avatar for leckie.
leckie

Posts: 896
Joined: 21 November 2008

Now, I've started on a bottle of red,but wouldn't parallel paths make the readings lower not higher?

Some meters read higher when operated on a no-trip setting.
 17 February 2013 10:58 PM
User is offline View Users Profile Print this message


Avatar for sparkingchip.
sparkingchip

Posts: 5296
Joined: 18 January 2003

Back to the OP:

"We know the meter can record readings through the CB and RCD, so gives a slightly false reading, but this was a lot higher than the true figure."