Job tomorrow as a favour for my dad.. Existing installation 30+ years old, 3036 fuses, customer doesn't want to have walls chopped etc, dads fitting a complete new bathroom including new electric shower... Shower is wired in 6mm but coming out the isolater is 2.5... Replacing the 2.5 for 6mm and sticking a rcd box (shower pack) at the bored.... Now there is a light in the bathroom she wants 6 down lights instead... How would you suggest I protect the lights, but the existing lighting circuit is pretty much nackerd?.?
|
|
|
|
|
|
|
|
|
RCD spur off the ring ?
|
|
|
|
|
|
|
|
|
Knackered how ? - and an RCD spur would solve most of your issues anyway as long as the existing bonding is up to scratch.
Regards OMS ------------------------- Failure is always an option |
|
|
|
|
|
|
|
|
No bonding... Rcd spur?
|
|
|
|
|
|
|
|
|
Put a 2 way RCD board in, 1 new shower, 1 new lighting cct for the bathroom. Henley block. Fix bonding.
If you go off the old board and the old installation is a pile of, you wil then be involved in a can of worms. New board removes you from the existing installation. ------------------------- ---------------------------------------- Lack of planning on your part doesn't make it an emergency on mine.... Every man has to know his limitations- Dirty Harry |
|
|
|
|
|
|
|
|
Was thinking of putting rcd box out side bathroom but lady doesn't want it
|
|
|
|
|
|
|
|
|
What lady wants, and what regs say!............................ just walk away and allow the local electrical village idiot do it, unfortunately it happens all the time these days!.
------------------------- Those who make no mistakes do very little work!!...... |
|
|
|
|
|
|
|
|
True Rulland, very true
|
|
|
|
|
|
|
|
|
6mm from the isolator if it's 2.5mm to the isolator won't help.
If it's 6 mm to the isolator from the CU then extend that 6mm into the new RCD 2-way shower unit next to the original board. Then take the existing lighting circuit from the old board and extend it into a 6A (if applicable, it probably is) MCB in the RCD'd shower unit as well. But you knew that anyway, didn't you ------------------------- S George http://www.state-it.com |
|
|
|
|
|
|
|
|
Fit ELV down lights fed via SELV transformers,no RCD protection required.Use the departures box on the cert to show a better level of protection than using an RCD.
------------------------- Regards Dave(not Cockburn) |
|
|
|
|
|