Topic Title: Meter Tails
Topic Summary: XLPE Tails
Created On: 09 February 2013 07:50 AM
statter
With the price of copper I was wondering why we dont see more use of 90 degree insulation which would allow tails to be 16mm2 rather than 25mm2 ? This would save a third of the copper and have plenty of margin on a 100A fuse for most installations.
I imagine that DNOs / meter companies might query this to start with but I dont see any technical objection. What am I missing?
 09 February 2013 08:39 AM
Jaymack
Velkommen to a virgin poster! The sharp bend for "90 degree" wouldn't be so kosher!
Seriously though, the equipment would also require a rating of 90°C
Sorry, couldn't resist - experience?
 09 February 2013 09:02 AM
I dont like the idea of running cables at 90 degrees in an uncontrolled domestic enviroment due to the risks of overheating if articles are stored against them, as is often the case,or if someone later encloses them.
And how hot would they get at 140 amps which the cut out fuse will pass for hours.
 09 February 2013 09:55 AM
. . . I imagine that DNOs / meter companies might query this to start with but I dont see any technical objection. What am I missing?
As Jaymack has already said, finding a CU rated for 90° would be interesting, plus you would not be able to have T&Es touching the tails, which could also be a challenge. Finally, as the DNO's fuse is protecting the tails from the meter to your CU (unless you have long tails, in which case it is to your overcurrent protection), they have a say in their size and construction.
 09 February 2013 11:30 AM
Avatar for UKPN.
UKPN
more importantly, the meter connection.
 10 February 2013 09:06 AM
statter
..... looks like a can of worms - probably why its not done. I haven't got a copy of the relevant BSs so cant see the temperature limitations on the individual MCBs, Isolators etc ditto for the meter.
I imagine a sustained 140A would destroy most 100A rated consumer units even with 25mm2 tails.
Thanks for the responses.