Topic Title: Metal Clad 13 Amp RCD Switch Fuse
Topic Summary: BS Number?
Created On: 08 February 2013 09:42 AM
Status: Post and Reply
Linear : Threading : Single : Branch
Search Topic Search Topic
Topic Tools Topic Tools
View similar topics View similar topics
View topic in raw text format. Print this topic.
 08 February 2013 09:42 AM
User is offline View Users Profile Print this message



tattyinengland

Posts: 782
Joined: 23 November 2006

Does anyone know the BS number for these RCDs?

Certification minor works blip - I need to issue this cert, but they are always checked by the clients M&E consultant, so need the correct number for sure.

Help appreciated as always.

Regards
Tatty
 08 February 2013 09:50 AM
User is offline View Users Profile Print this message


Avatar for OMS.
OMS

Posts: 19602
Joined: 23 March 2004

BS 1363 - 4 and BS 7288

OMS

-------------------------
Failure is always an option
 08 February 2013 09:55 AM
User is offline View Users Profile Print this message



tattyinengland

Posts: 782
Joined: 23 November 2006

Thank you OMS - is that an either/or reply?

It's either BS 1363 or it is 7288 depending on the manufacturer?

On my drop down menu - using easy cert - it has both options for the BS number of an RCD.
 08 February 2013 10:00 AM
User is offline View Users Profile Print this message


Avatar for OMS.
OMS

Posts: 19602
Joined: 23 March 2004

It's a both - the fused spur is in accordance with BS 1363-4 and the RCD protection is usurped from the standard for SRCD's ie BS 7288.

If you are making a claim on the RCD, then I'd go with BS 7288 (don't know if you can add a note to Eastcert to clarify ?)

Does your software list include IEC 62640 ?

Regards

OMS

-------------------------
Failure is always an option

Edited: 08 February 2013 at 10:06 AM by OMS
 08 February 2013 10:23 AM
User is offline View Users Profile Print this message



tattyinengland

Posts: 782
Joined: 23 November 2006

HI OMS

Thank you. 7288 it is then.

The soft ware does not include 62640, nor is it a number that I am familiar with - I had to google it!

For those that are interested:

IEC 62640:2011 applies to residual current-operated devices (RCD) incorporated in, or specifically intended for use with two pole socket-outlets, with or without earthing contact for household and similar uses (SRCD: socket-outlet residual current devices). SRCDs, according to this standard, are intended to be used in single phase systems such as phase to neutral or phase to phase or phase to earthed middle conductor. SRCDs are only intended to provide additional protection downstream of the SRCD. SRCDs are intended for use in circuits where the fault protection (indirect contact protection) is already assured upstream of the SRCD.
 08 February 2013 11:08 AM
User is offline View Users Profile Print this message


Avatar for OMS.
OMS

Posts: 19602
Joined: 23 March 2004

I guess you need to decide what protection the spur is providing - I would assume "additional protection" only ?

Regards

OMS

-------------------------
Failure is always an option