Topic Title: TN-S converted to TT?
Topic Summary: Why?
Created On: 06 February 2013 07:20 AM
SherlockOhms
Chaps,
I spotted the above conversion whilst looking at a job yesterday.
The service head was clearly that of a TN-S supply complete with earth clamp, allbeit a 951 type and yet, the main earth cable was disconnected and terminated outside to an earth rod.
Any clues as to why this may have been done.?
If there is a problem with the supply cable then the DNO should rectify?
Just for a bit of added comedy, on the same job, the electric shower was fed from the light switch in the airing cupboard in 1,5mm. No RCD in the building. A new personal best I think?
The subsequent phone conversation with the landlady began "Are you sitting down?".
S.
 06 February 2013 07:31 AM
primo
I've had to make a couple of TN-S supplies TT due to poor readings (in fact no reading on one of them) on the supply cable sheath. When the customers found out about the upheaval of having their front gardens dug up to replace the supply cable they opted for the rod instead. In both cases I left the old TN-S earth connection if only to serve as main bonding to the supply cable.
 06 February 2013 08:49 AM
Grumpy
I had one recently where checks before a board change showed 0.7 ohms but had risen to several hundred after board change a week later. Didn't need to TT as nice SSE came out and PME'd it. He suggested lead sheath had split where it joined main supply in the street. As above bonding left to sheath.
 06 February 2013 08:50 AM
Parsley
The DNO only has to maintain the earth if they provided the earth in the first place, as there is a 951 clamp fitted maybe they didn't.
 06 February 2013 11:20 PM
peteTLM
Haha! Where i live is the old eastern electricity board area and there are literally millions of houses with them fitted by the DNO.
P
 06 February 2013 11:51 PM
Yes next door to my area (The old YEB) are fitted some inferior (Prior BS 951) earth clamps on the lead sheath. Just about one up from a buckle clip. Current carry capacity about the same as a paperclip I suspect.
At least my old area (Norweb) had sweated joints (OK not much bigger than 30A fusewire I admit. LOL