Topic Title: Screwfix LAP Double Sockets
Created On: 04 February 2013 03:56 PM
Richard64
Had a job 3 weeks ago to replace some sockets that had started to fail. Mainly on one of the neutrals.
Screwfix had sent replacements, and I had to swap them over and supply MWCs as part of the guarantee.
I've just been informed that one of the new ones has gone the same way.
R1 and R2 readings were all fine.
Any ideas or are they just rubbish sockets?
 04 February 2013 04:04 PM
Sounds likely....
Why do we never check N continuity/resistance? (Rn) I realise a bad N isn't a shock risk (unlike L & PE/R1&R2), but isn't it a overheating/fire/burn risk still?
 04 February 2013 04:08 PM
Richard64
Andy.
Sorry, should have said R1 + R2
The r1 r2 and rn readings were fine too.
Just wondering if a poor connection in one of his plug tops could be causing this. The failure has only been one side of the double socket.
 04 February 2013 04:16 PM
Ricicle
What sort of load is plugged into the socket(s) ?
 04 February 2013 04:23 PM
Richard64
I'm not sure.
I've just emailed him to ask if there have been any common denominators.
 04 February 2013 09:03 PM
Avatar for Martynduerden.
Martynduerden
LAP LOUSY AND PROBLEMATIC, it's all in the name
Try MK MAINLY KOOL and on £2.60 !!
Crabtree sorry no imagination left
Cheap IS expensive !
Martyn.
 04 February 2013 10:17 PM
Avatar for sparkingchip.
I have just used some LAP brushed stainless fittings for the first and last time.
I had to return a 20A switch with neon and a three gang light switch as they had faulty switches straight away as they never work, so they are off the list of approved products now.
Andy
 04 February 2013 10:42 PM
Martynduerden
Does it matter?
We cannot control what is plugged in nor should we try.
I assume its a standard 13A plug with an unbriged fuse of any rating?
Out of Interest what do they cost ?
Martyn.
 04 February 2013 11:01 PM
That is a distinct possibility, i've seen this a number of times,
 05 February 2013 10:25 AM
Richard64
I'm guessing it's the sockets.
The fella fitted them last year ands when they devoloped the faults contacted screwfix.
They sent him replacements and agreed to pay an approved electrician to fit them and supply MWCs.
That's when he contacted me.
As I said, on both circuits the end to ends, r1 and rn where about the same give or take 0.01 ohm and r2 was just over half again. So no loose connections. And R1+R2 was consistent with these figures.
It's the neutral on one of the outputs, not both which makes me think it's a faulty batch. Or, again a bad plug connection.
The sockets did look rather crap though.
On a brighter note, he's a foreign chap, New Zealander, without our British sensibilities about complaining. So some poor sod at screwfix may well have his day ruined. :-)
 05 February 2013 01:07 PM
Ricicle
Does it matter?
I asked because even MK plug and socket combinations won't run with constant loads at or near 13A. With cheaper sockets the detoriation might be even quicker !
 05 February 2013 01:24 PM
Richard64
Does it matter?
Really? I've never heard of that. And I've seen plenty of Immersion heaters and cookers on plug tops.
If a 13A socket outlet can't take 13A, that's a pretty poor design.
Especially when you can pull more than 13A through a 13A fuse for quite some time.
 05 February 2013 01:38 PM
It is very common knowledge in the electrical trade, in fact it's usualy the fuse holder that overheats and causes the damage, very common on fcu's feeding immersion heaters,
 05 February 2013 01:43 PM
Richard64
Well. That's something I've never considered. Although, I prefer to put immersions on DP switches.
And I've seen burnt out FCUs. But that's generally poor connections.
Still, a very bad design flaw though.
 05 February 2013 01:55 PM
rogerbryant
I posted this last year on the joys of fused plugs :-)
http://www.esc.org.uk/fileadmi...-lead-test-report.pdf
Best regards
Roger
 05 February 2013 02:22 PM
Possibly a feature of the ambient temperature of the airing cupboard - I think BS 1363's conditions for ambient temperature are quite restrictive.