okay two port valves have 5 stinking wires coming out of them.
Concentrating on the grey and orange.. ..why do they make it with a grey (perm live), when they could just use the brown as the live feed on the microswitch. |
|
|
|
|
|
|
|
|
Because if you had more than one it would latch on and not turn off!
|
|
|
|
|
|
|
|
|
|
|
|
|
|
|
|
|
|
Because if you had more than one it would latch on and not turn off! Can you explain please, I don't follow you. What I'm asking is why doesn't the (stat controlled) brown act as the supply to the micro-switch? |
|
|
|
|
|
|
|
|
Because if you have the oranges from two or more connected together to feed a boiler when one thermostat stops calling for heat, before the spring can release the valve, it will stay open fed from the other valve's brown supply through it's own contacts.
(edit: did do a drawing with characters but it didn't post properly) Does that help ?? (About time we could upload diagrams, being as it's a technical forum) Stu |
|
|
|
|
|
|
|
|
Because if you had more than one it would latch on and not turn off! Can you explain please, I don't follow you. What I'm asking is why doesn't the (stat controlled) brown act as the supply to the micro-switch? The brown motor wire would pick up a live back through the micro switch form any other valve on the heating system. Would act like a latch on a relay. |
|
|
|
|
|
|
|
|
Because if you have the oranges from two or more connected together to feed a boiler when one thermostat stops calling for heat, before the spring can release the valve, it will stay open fed from the other valve's brown supply through it's own contacts. Hi Stu are you trying to say what colin said: The brown motor wire would pick up a live back through the micro switch form any other valve on the heating system. Would act like a latch on a relay. |
|
|
|
|
|
|
|
|
(About time we could upload diagrams, being as it's a technical forum) Stu Agreed. Lets start a topic. |
|
|
|
|
|
|
|
|
You could always link your grey to the brown, assuming you only have one valve.....
Its all about options, you really would be complaining if you only had 4 wires! ------------------------- Regards Martyn. Only a mediocre person is always at their best www.electrical contractors uk.com |
|
|
|
|
|
|
|
|
Because if you have the oranges from two or more connected together to feed a boiler when one thermostat stops calling for heat, before the spring can release the valve, it will stay open fed from the other valve's brown supply through it's own contacts. Hi Stu are you trying to say what colin said: The brown motor wire would pick up a live back through the micro switch form any other valve on the heating system. Would act like a latch on a relay. Yes |
|
|
|
|
|
|
|
|
okay well you've cleared something up there that's bugged me for ages!! I suppose I have only ever thought of it in the context of one valve...
You could always link your grey to the brown, assuming you only have one valve..... Its all about options Thanks guys. Just took the kids to Frankie & Benny's - £220. I thank you! |
|
|
|
|
|
|
|
|
I remember some years ago on a system I was working on for some heating bods the valves were only four wire (the L for the feed for the "Turned" microswitch was derived from the L of the valve.
Ended up putting them a relay for each valve for zoning (any valve opened fired up the pump ------------------------- Regards, Ebee (M I S P N) Knotted cables cause Lumpy Lektrik |
|
|
|
|
|