Topic Title: Domestic Fire Alarm Wiring
Topic Summary: On 2 circuits
Created On: 17 January 2013 04:28 PM
ohmer
I have come across a domestic installlation where the smoke detectors are wired on 2 circuits with a single signal cable linking them. I cant find a reg to say this is wrong. It does not seem correct to me. Any one got any thoughts.
Ohmer
 17 January 2013 04:47 PM
Avatar for slittle.
I wouldn't have done it. Usually the link cable is referenced to neutral so there is a good chance of a borrowed neutral between the two circuits
 17 January 2013 08:13 PM
ohmer
I did not carry out this work, but also feel it is wrong. I need to find a regulation so that I can rectify this. Any reg I can use??
 17 January 2013 08:48 PM
andrew331
ohmer,
It will contravene 134.1.1 if not installed in accordance with the manufacturers instructions.
 17 January 2013 10:52 PM
Avatar for sparkiemike.
sparkiemike
I won't comply with BS5839 part 6, clause 15.5 (b)
Power supplies for Grade D systems
b) If smoke alarms and any heat alarms are of a type that can be interconnected by wiring, all smoke alarms and heat alarms should be connected on a single final circuit.
NOTE This recommendation does not apply if the form of interconnection is not capable of conducting current, e.g. if the means of interconnection comprises radio communication rather than wiring.
 17 January 2013 10:55 PM
I'd go for a contravention of 314.4 (second sentence).
 17 January 2013 11:04 PM
DOUGIE1000
a easy fix would be to fit two radio smokes,
Dougie
Power Plus Electrical.co.uk