Topic Title: Advice needed
Topic Summary: Change of use of cable
Created On: 15 January 2013 09:53 AM
Hayeso32
Hi all. I need some advice!!
I am working on a site which has 2 supplies to 2 outbuildings. They are fed via 2 core 6mm swa's.The outbuildings are been changed to now have power within them as well as the existing lighting. A local db is to be installed in each one suppling a camera,heater,auto door and lights.Total load in each one will be no more than 3000w.The dno supply is tn-s. The protective device will be 32a type c. To settle a disagreement- is the armouring suitable as the earthing conductor or does it need to be done as a (tt) installation?
 15 January 2013 10:04 AM
John Peckham
PM me your email address and I will send you the information you need.
John Peckham
 15 January 2013 10:56 AM
Any extraneous-conductive-parts?
 15 January 2013 08:44 PM
Hayeso32
No - only exposed conductive parts. Surface galv conduit installation!!
 15 January 2013 09:55 PM
John Peckham
I cannot send anything back to you on the email address you sent. Can you resend from your computer not your Iphone.
John Peckham