A small foyer area leads to the original bathroom (there probably was an interconnecting door, but that been removed).
I am only there to re-connect a new shower in the same position etc. So I have allowed for an RCD for the shower. Today they asked me to fit some suitable bathroom light fittings... The light in the foyer and the light in the bathroom come off the same switch on the wall inside the foyer (well outside the zones - 2.6m actually)... which upon inspection, has no rcd. So, am i correct to assume i can leave the switch where it is, but i must add rcd for that whole lighting circuit and Regards Ady ------------------------- Resistance is futile. |
|
|
|
|
|
|
|
|
As long as the circuits satisfy the requirements for ADS, are provided with 30mA RCD protection, and all extraneous-conductive-parts are effectively connected to the main bonding, supplementary bonding would not be required.
|
|
|
|
|
|
|
|
|
You copy that out the book spin
------------------------- Resistance is futile. |
|
|
|
|
|
|
|
|
No, I made it all up myself.
|
|
|
|
|
|
|
|
|
ok mate, thanks
only messin. ------------------------- Resistance is futile. |
|
|
|
|
|
|
|
|
That's the tricky one. With the traditional British hot water system - with hot water supplied at low pressure from a cylinder supplied from a plastic supply tank, there's often no direct connection between the hot water pipework and the main bonding (the plastic tank gets in the way). - Andy. |
|
|
|
|
|
|
|
|
Not that tricky.
Nothing a bit of supplementary bonding won't sort out. |
|
|
|
|
|
|
|
|
Andy, I have a similar situation where there is a Megaflow system in use, would this mean all the pipework has continuity to the main incomer and bonding? (all pipework is copper)
Apologies for hi-jacking your thread Ady! Dave. |
|
|
|
|
|
|
|
|
That's the tricky one. With the traditional British hot water system - with hot water supplied at low pressure from a cylinder supplied from a plastic supply tank, there's often no direct connection between the hot water pipework and the main bonding (the plastic tank gets in the way). - Andy. What about the metal boiler? |
|
|
|
|
|
|
|
|
Conventional system (non-combi) boilers don't have a direct connection to the cold water pipe - they're conventionally fed from another plastic feed & expansion tank, so unless someone has considered the heating flow & return pipes to be extraneous from the point of view of the entire installation (which they're usually not) and main bonded them, there's still no direct connection to the main bonding. - Andy. |
|
|
|
|
|
|
|
|
Conventional system (non-combi) boilers don't have a direct connection to the cold water pipe - they're conventionally fed from another plastic feed & expansion tank, so unless someone has considered the heating flow & return pipes to be extraneous from the point of view of the entire installation (which they're usually not) and main bonded them, there's still no direct connection to the main bonding. - Andy. You will probably get a connection through the gas bond. ------------------------- Specialised Subject. The Bleedin Obvious. John Cleese |
|
|
|
|
|
|
|
|
Possibly, but we're banned from selecting gas (or oil) pipes as protective conductors (543.2.3) - Andy. |
|
|
|
|
|
|
|
|