Topic Title: 3-phase cut-out in a park
Topic Summary: where is fed from?
Created On: 04 January 2013 06:26 PM
aargeitakis
Hi
i ve been asked to go and check a 3-phase cut-out in a park.
The 3-phase cut-out(head) is in the middle of a park in a steel box(like a small telephone box). I checked all phases and they are dead.
They have new boxes now installed in the park and they want to remove this old one. They want to cut the cable and remove the box.
They believe that this head is fed from a BD in a building/shed in the park which we did have access yet.
I believe that this head is property of the Western power and they have to deal with it. I dont think you can have a head as a part of a privite installation and fed from a DB.
Paul
 04 January 2013 06:29 PM
sparkxelectrical
what cable type supplies it?
 04 January 2013 06:36 PM
DOUGIE1000
Supplier will know more I would imagine
Dougie
Power Plus Electrical.co.uk
 04 January 2013 07:01 PM
aargeitakis
The cable comes underground.
The outsheath is the classic supplier cable, bitumen/cloth finishing, 40-50mm thick. I ll say 4-core 35mm2.
 04 January 2013 10:50 PM
Avatar for slittle.
I'd chuck it at the utility (WPD) given the cable type etc.
That said, we've used cut-outs as demarcation lots of times on farm networks so it could be private and just old. sounds like PILCSWA or similar if it's cloth covered.
 05 January 2013 12:43 AM
Depending on the area, it could be PILCSWA or PILCSTA construction. As others have said, you should refer it to the DNO first - Western Power in your case. It is possible that the supply is for public lighting. In this case, it may be charged based on the number of lamps connected, rather than being a metered supply. The DNO may also have control gear that only energises it at certain times of the day.
 05 January 2013 10:54 AM
aargeitakis
Thanks for your replies everybody