Topic Title: Advice Please Topic Summary: first assessment. Created On: 31 December 2012 06:19 PM Status: Post and Reply |
Linear : Threading : Single : Branch |
Search Topic |
Topic Tools
|
|
|
|
|
Just fitted new 17th edition CCU, two D/G sockets and two new extra lights under MW. I know I have to issue EIC for the new
CCU , my question is can I add two D/G sockets and two extra lights as part of the EIC or not. If not will I need to issue a MWC for each socket and lighting point. Your advice would be appreciated as it is going towards my first assessment. Many thanks Nedd. |
|
|
|
|
|
|
|
|
Put it all on the EIC Nedd, and please don't call a consumer unit a CCU, that makes it sound like a cooker control unit! Btw, if you did use a MWC you only have to issue a seperate one for each circuit worked on, not each accessory,
Good luck with the assessment, Dave. |
|
|
|
|
|
|
|
|
"Just fitted"
As a replacement item? Regards BOD |
|
|
|
|
|
|
|
|
Put it all on the EIC Nedd, and please don't call a consumer unit a CCU, that makes it sound like a cooker control unit! Btw, if you did use a MWC you only have to issue a seperate one for each circuit worked on, not each accessory, Good luck with the assessment, Dave. |
|
|
|
|
|
|
|
|
Just another thought Nedd, you don't need to mention the sockets if they are just replacements but the additional lights should be either on mwc or in this case on your eic as you're doing one anyway,
Dave. |
|
|
|
|
|