Topic Title: 4 wire zone valve
Created On: 29 December 2012 12:45 PM
SKElectrical
Having left my testers at a client's house, I couldn't test voltages on this one...
working on a zone valves, some of them had 4 wires coming out of them - will these have been low voltage valves?
 29 December 2012 12:51 PM
colinhaggett
As in a normal domestic heating system? Brown, Blue, Grey & Orange?
 29 December 2012 01:38 PM
SKElectrical
No it was commercial.
Domestically you would have green/yellow as well.
The colours on this valve were: brown, blue, green/yellow, and black.
I'm thinking low voltage (2 for motor & 2 for microswitch and no cpc).
Valve approx. 15yr old
 29 December 2012 01:56 PM
colinhaggett
Might be motor open/ motor close?
I'd go for Brown (live and motor drive)
Blue netural
Green/Yellow CPC
Black switched live from the brown
There are a lot of new valves about without a CPC on them too. many of the newer ones are all plastic case and hence four wires
 29 December 2012 01:59 PM
colinhaggett
Their is at least one make that doesn't have a earth wire!
 29 December 2012 02:13 PM
briandoherty
You call it a 'zone valve' but as you're in a commercial environment it may be a three-position control valve with, as colinhaggett suggested, 'motor open / motor close'. In this case, it is likely brown to drive motor one way, black to drive motor the other way, blue for neutral and green/yellow for earth. These valve actuators can position the valve anywhere between the two extremes as required for control.
Brian
 29 December 2012 03:34 PM
Opps, missed the bit about commercial in the OP.
Yep, i'll go with open/close in that case
 29 December 2012 07:40 PM
chunk522
Ive had these where the blue and the black are both switched lives if this helps