 22 December 2012 10:05 PM
User is offline View Users Profile Print this message



ameen1702

Posts: 3
Joined: 21 December 2012

the situation when a submain distribution board is supplied from a main distribution board.
is it necessary that the smdb has a main cb (or fuse) at its incoming.
i have seen some designs with identical cbs at the outgoing of the mdb and the incoming of the smdb.in this case ,what is the purpose of the cb at the incoming of the smdb as the cable will be protected by the cb at the mdb.
in other designs ,there is a main switch not cb at the incoming of the
smdb , this arrangement seems logical for more economy,
the question is ,is it nessary that every distribution board has a main cb , or a main switch will be enough,
please excuse my poor english.
 23 December 2012 08:21 AM
User is online View Users Profile Print this message


Avatar for leckie.
leckie

Posts: 1966
Joined: 21 November 2008

There is no requirement for an additional circuit breaker at the sub db
 24 December 2012 02:17 PM
User is offline View Users Profile Print this message



ameen1702

Posts: 3
Joined: 21 December 2012

thanks for replying, another question please, when a 3 pole cb rated 150 amp ,does it mean 50 amp per pole or the 150 amp is the sum of them all.
 24 December 2012 06:19 PM
User is offline View Users Profile Print this message


Avatar for Rulland.
Rulland

Posts: 481
Joined: 11 April 2008

A 3 phase cb is rated per pole-ie a 32A triple is 32A per phase.
Your post above should say 50A per pole or 150A per pole.

-------------------------
Those who make no mistakes do very little work!!......
 25 December 2012 04:23 PM
User is offline View Users Profile Print this message



ameen1702

Posts: 3
Joined: 21 December 2012

yes, you're right,that was a mistake.
and thanks a lot for replying.
 25 December 2012 05:00 PM
User is offline View Users Profile Print this message


Avatar for Rulland.
Rulland

Posts: 481
Joined: 11 April 2008

Merry Christmas, you're welcome.

-------------------------