Cable Capacitance Test
650V IT Distribution System

Can anyone advise on a correct method for this test.
 07 December 2012 06:49 PM
User is offline View Users Profile Print this message



rocknroll

Posts: 9541
Joined: 03 October 2005

I presume from your post this is a medical location???, cable capacitance testing is unfortunately a very inaccurate science even under laboratory conditions, the equipment you need for this is a capacitance bridge that is capable of measuring within 0.01% of absolute value, my advice would be to run this through the cable manufacturer first as they might have values available, you can get capacitance meters and they tend to be rack mounted and expensive.

regards

-------------------------
"Take nothing but a picture,
leave nothing but footprints!"
-------------------------
"Oh! The drama of it all."
-------------------------
"You can throw all the philosophy you like at the problem, but at the end of the day it's just basic electrical theory!"
-------------------------

Edited: 10 December 2012 at 12:45 AM by rocknroll
 07 December 2012 07:16 PM
User is offline View Users Profile Print this message



OMS

Posts: 22359
Joined: 23 March 2004

I doubt it's medical Rock - not at that voltage

MEiGan doesn't call up capacitive testing as the limit if for 10kVA per system so capacitive coupling will be low.

650V, ITearthed sounds industrial to me - you need knowledge of the cable capacitance because you don't have solid earthing (it will influence the earth fault current)

Regards

OMS

-------------------------
Let the wind blow you, across a big floor.
 09 December 2012 10:53 PM
User is offline View Users Profile Print this message



paulskyrme

Posts: 1285
Joined: 12 February 2003

I'd guess @ 650V it would be railway related?...
 09 December 2012 11:56 PM
User is offline View Users Profile Print this message



alancapon

Posts: 6879
Joined: 27 December 2005

I believe the London Underground traction supply is a 630v dc IT system with earth monitoring. In some stations, the lift and escalator supplies are taken from the traction supply.

Regards,

Alan.
 10 December 2012 12:19 PM
User is offline View Users Profile Print this message



Inrush

Posts: 741
Joined: 19 December 2007

Judging by the voltage I would guess this is probably a non-earth referenced Network Rail signalling feeder.

you need knowledge of the cable capacitance because you don't have solid earthing (it will influence the earth fault current)


Yes, I would think the OP is trying to determine the touch voltage under 1st earth fault conditions.