Topic Title: Cable trench for DC cables
Topic Summary:
Created On: 05 December 2012 03:10 PM
Status: Post and Reply
Linear : Threading : Single : Branch
Search Topic Search Topic
Topic Tools Topic Tools
View similar topics View similar topics
View topic in raw text format. Print this topic.
 05 December 2012 03:10 PM
User is offline View Users Profile Print this message


Posts: 3
Joined: 10 May 2012

I would appreciate if someone could provide some standards regarding the installation (e.g clearance) of DC power cables buried in a trench.

Are they any specs when installing lots of DC power cables in the same trench?
 05 December 2012 03:21 PM
User is online View Users Profile Print this message


Posts: 12901
Joined: 13 August 2003

what sort of voltages are we talking about?
- Andy.
 05 December 2012 03:56 PM
User is offline View Users Profile Print this message


Posts: 20560
Joined: 23 March 2004

Keep +ve and -ve close together (for each circuit) - ideally use earthed metal containment (SWA cable is ideal) to get a bit of inductance to damp potential inductive surges . Then provide seperation of at least 2 x cable diameter from each circuit.

Personally, I'd be using a pit and duct system with min 100mm dia ducts - one per circuit

Use labelling tapes warning of what's below if you do bury direct or the same above the duct if you go that way