-------sne type cut-outs installed in blocks of flats have led to confusion
over earthing systems.

it is possible to find SNE (separate neutral and earth) cut-outs installed
by other parties in blocks of flats that are fed from the distribution PME
point of supply. the link (neutral and earth) must not be closed in a SNE
cut-out.

UKPN are a DNO and their work must comply with the ESQCR regs
and their responsiblity ends at the intake position.
the BNO is then responsible for the rising mains and cut outs/red links.
all BNO work must come under the current version of BS7671 and
a combined N+E is not allowed.

Regards.

is your consultant giving dodgy advice-like you dont have to main bond
services anymore?
well---who do you trust!
 29 November 2012 09:29 PM
User is offline View Users Profile Print this message


Avatar for slittle.
slittle

Posts: 3613
Joined: 22 November 2007

I've been sent a rather large document by the ECA which details UKPN's earthing arrangements going forward.

It seems like sensible guidance from what I've digested so far.



Stu
 29 November 2012 09:54 PM
User is offline View Users Profile Print this message


Avatar for UKPN.
UKPN

Posts: 552
Joined: 17 January 2012

----always glad to be service young man.

Regards.
 29 November 2012 09:56 PM
User is offline View Users Profile Print this message


Avatar for Parsley.
Parsley

Posts: 1135
Joined: 04 November 2004

Originally posted by: slittle

I've been sent a rather large document by the ECA which details UKPN's earthing arrangements going forward.



It seems like sensible guidance from what I've digested so far.


Stu

I think OMS posted the link to the document a few weeks ago, do you like the the new PME customers responsibility labels?

Regards




Stu
 29 November 2012 09:59 PM
User is offline View Users Profile Print this message


Avatar for OMS.
OMS

Posts: 19964
Joined: 23 March 2004

Are you on a journey of rediscovery UKPN

is your consultant giving dodgy advice-like you dont have to main bond services anymore?
well---who do you trust!


LoL - now did I say that ? - wasn't it actually regarding bonding a plastic water main - do try and keep up, there's a good fellow

Regards

OMS

-------------------------
Failure is always an option
 29 November 2012 10:06 PM
User is online View Users Profile Print this message


Avatar for rocknroll.
rocknroll

Posts: 8920
Joined: 03 October 2005

Oh dear!!!!!

According to my information the BNO work must becarried out in a safe and competent manner to a level complying with or exceeding the requirements of health & safety and electricity related legislation and, in particular, relevant requirements of the Electricity Act 1989 (as amended), the Utilities Act 2000, Electricity At Work Regulations 1989 (as amended) and the Electricity Safety, Quality and Continuity of Supply Regulations 2002, from a legal standpoint BS 7671 only applies from the seal postion are you getting this mixed up with the installation they connect to must be compliant to BS7671.

regards

-------------------------
"Take nothing but a picture,
leave nothing but footprints!"
-------------------------
"Oh! The drama of it all."
-------------------------
"You can throw all the philosophy you like at the problem, but at the end of the day it's just basic electrical theory!"
-------------------------
 29 November 2012 10:17 PM
User is offline View Users Profile Print this message


Avatar for UKPN.
UKPN

Posts: 552
Joined: 17 January 2012

----I never get mixed up fella!

Regards.
 29 November 2012 10:20 PM
User is offline View Users Profile Print this message


Avatar for OMS.
OMS

Posts: 19964
Joined: 23 March 2004

Really ?

OMS

-------------------------
Failure is always an option
 29 November 2012 10:23 PM
User is offline View Users Profile Print this message


Avatar for leckie.
leckie

Posts: 2182
Joined: 21 November 2008

UKPN
I've sent lots of posts on the water bond post.

Your saying it should be bonded, others say no.

Have a read of mine and give your opinion, with some reasoning if possible
 29 November 2012 10:24 PM
User is offline View Users Profile Print this message


Avatar for leckie.
leckie

Posts: 2182
Joined: 21 November 2008

Hurry up though because I've scrapped most of my 10mm green yellow and am about to throw the lot out tomorrow!
 29 November 2012 10:35 PM
User is offline View Users Profile Print this message



AJJewsbury

Posts: 11910
Joined: 13 August 2003

Does that mean the DNOs have given up running CNEs to each flat (i.e. using the gas pipes as parallel N conductors) at long last?
- Andy.
 29 November 2012 10:37 PM
User is offline View Users Profile Print this message


Avatar for OMS.
OMS

Posts: 19964
Joined: 23 March 2004

Originally posted by: AJJewsbury

Does that mean the DNOs have given up running CNEs to each flat (i.e. using the gas pipes as parallel N conductors) at long last?

- Andy.


Ouch -

OMS

-------------------------
Failure is always an option
 29 November 2012 10:38 PM
User is offline View Users Profile Print this message


Avatar for OMS.
OMS

Posts: 19964
Joined: 23 March 2004

Originally posted by: leckie

Hurry up though because I've scrapped most of my 10mm green yellow and am about to throw the lot out tomorrow!


Perhaps best to keep just a bit, Leckie - you never know when it just might be extraneous -

regards

OMS

-------------------------
Failure is always an option
 29 November 2012 10:46 PM
User is offline View Users Profile Print this message


Avatar for leckie.
leckie

Posts: 2182
Joined: 21 November 2008

No , sorry it's too late now. Henceforth if I see any clamps on a water pipe with a plastic incomer I'm going to give it a code1!

I'm going to re-read gn8 this weekend just to make sure though. I've got the old gn8. Is he new one a big improvement?
 29 November 2012 10:50 PM
User is offline View Users Profile Print this message


Avatar for OMS.
OMS

Posts: 19964
Joined: 23 March 2004

LoL - don't you trust me

Steady on the Code 1 though - what regulation does it contravene ?

I've not read the new published verison to be honest - a version I did see wasn't significantly different

regards

OMS

-------------------------
Failure is always an option
 29 November 2012 10:58 PM
User is offline View Users Profile Print this message


Avatar for leckie.
leckie

Posts: 2182
Joined: 21 November 2008

It contravenes oms law
 29 November 2012 11:01 PM
User is offline View Users Profile Print this message


Avatar for UKPN.
UKPN

Posts: 552
Joined: 17 January 2012

tomorrow-like every day since the mid-sixtys electricians
all over our land will accept the advice of their DNO/Meter op
and bond to their requirements.
I enjoy these topics but I cannot quote non-statutory books
to my customers. the wiring regs are not an act of parliament
and the guides are generally helpful but to hear posters saying
the words like "rules" is a step too far.

tomorrow all over this land our customers electricians will
bond main services regardless of if they are plastic origin.

millions of them have followed this advice and will continue into
the future.

and we have only been discussing water/gas, there are many
more.

I have NEVER had a contractor dispute my earthing advice
and talking about "more than 22k" and "low risk" "how many shocks have there been anyway" is rediculous.

UKPN will look after you!

Regards.
 29 November 2012 11:22 PM
User is offline View Users Profile Print this message


Avatar for OMS.
OMS

Posts: 19964
Joined: 23 March 2004

You heard it here first folks - Sweet 'n Sour Light and Power - the guys who told you to bond plastic pipes -

Regards

OMS

-------------------------
Failure is always an option
 29 November 2012 11:29 PM
User is online View Users Profile Print this message


Avatar for rocknroll.
rocknroll

Posts: 8920
Joined: 03 October 2005

I spent enough time in the past with you lot, DNO's, what about that clause in the agreement between the customer and the appropriate electricity board which states, please note that our employees and contractors are not qualified to advise on electrical installation matters, and then it goes on to say you need to contact a qualified electrician to inspect the installation and advise on earthing and bonding, or did you get mixed up about that one as well.

regards

-------------------------
"Take nothing but a picture,
leave nothing but footprints!"
-------------------------
"Oh! The drama of it all."
-------------------------
"You can throw all the philosophy you like at the problem, but at the end of the day it's just basic electrical theory!"
-------------------------
 29 November 2012 11:29 PM
User is offline View Users Profile Print this message



John Peckham

Posts: 7721
Joined: 23 April 2005

"i enjoy these topics but I cannot quote non-statutory books".

No doubt that is your personal preference UKPN but the current UKPN Earthing Manual does quote from BS7671.

-------------------------