I am in the process of fitting out a new training classroom in which it has already been decided to fit 40no 600x600 4x 18w T5 HF modulars. It is a large room and may be occupied by a small number of people who may be relatively immobile. I was wondering if any one could recommend a reliable occupancy sensor?
Client not interested in dimming etc, only compliance with Building Regs. ------------------------- Regards, Lyle Dunn |
|
|
|
|
|
|
|
|
Danler, Steinel, Lutron
|
|
|
|
|
|
|
|
|
Split it into groups perhaps Lyle - it'll be a hell of a good sensor if it can cope with bang switching of 40 No 4 x 18W HF fittings on multiple circuits (and at 2.4 centres is going to be bloody bright as well)
Split it into roughly 40m2 sections would be my advice. Or put in a cheap LMS controller via marshalling boxes - one PIR per say 9 luminaires regards OMS ------------------------- Failure is always an option |
|
|
|
|
|
|
|
|
Nail on the head
|
|
|
|
|
|
|
|
|
I would have thought that if its one room with people with limited mobility then all lights would require to be illuminated at the same time
So if thats the case you would really want a control circuit for the PIR's to switch contactors to control each circuit Danlers recommend a grid layout with spacing at 5m. |
|
|
|
|
|
|
|
|
If you want a simple system that will deal with absence or occupancy switching, manual control if required, link groups or corridor hold, emergency lighting connection and test in a fit and forget box that's quick to install, then try the KliK system from Hager.
9 luminaires will serve an area of about 35m2 so zoning to 40m2 as my suggestion is easy. You can configure that any PIR brings on the whole room, just the group or will also trigger the adjoining group to avoid users sitting in a small pool of light at times of partial occupancy If there is adequate daylight, I'm suprised at no daylight linking for dimming but the PIR's also have a photocell that will turn off luminaires if adequate daylight is present. We've specified a few and no reports of problems Regards OMS ------------------------- Failure is always an option |
|
|
|
|
|
|
|
|
Thanks guys, I was really only looking for a recommendation for a simple presence detector. Really fed up with poor quality / faulty products recently even from the well-known brands.
The detectors will be in parallel and control a governing contactor which in turn will serve 6 lighting circuits via relays and local switches. ------------------------- Regards, Lyle Dunn |
|
|
|
|
|
|
|
|
LoL
OMS ------------------------- Failure is always an option |
|
|
|
|
|
|
|
|
LoL; Is that lots of love or laugh out loud?. Leveson has thrown me in to a state of confusion! I hear Nick is suggesting that Dave regulates against its use just so that such things are not mis-interpreted, just like some posts!
------------------------- Regards, Lyle Dunn Edited: 29 November 2012 at 10:46 PM by lyledunn |
|
|
|
|
|
|
|
|
lets try LMFAO then Lyle -
just be a bit mindful of the inrush if the whole lot starts in one go from a contactor - 40 No 4 x 18w will be a bit of crack for sure OMS ------------------------- Failure is always an option |
|
|
|
|
|
|
|
|
Yep OMS acknowledge that, cheers. Probably best to have at least a couple of contactors to, dare I say it, spread the crack.