Could someone enlighten me as to an easy rule of thumb for the need to upgrade from a B to a C type circuit breaker?
This is specifically for commercial flourescent lighting. The current lighting is 6 x 80w 6' tubes, to be replaced by 6 x double 70w fittings.

It is currently protected by a 6A type B.

So, I am, roughly, doubling the current usage, so using 1.8 x the rated current, this gives 1512 watts/ ~ 6.6A, so the CB needs to be uprated, which isnt a problem, as it is run in 1.5mm T+E.

The lights I am fitting give no indication of any 'inrush' current, so what factor is used to determine if a C type CB is required?
Thanks
Alan.
 28 November 2012 09:40 PM
User is offline View Users Profile Print this message


Avatar for leckie.
leckie

Posts: 1605
Joined: 21 November 2008

Time/ current graphs
 28 November 2012 09:41 PM
User is offline View Users Profile Print this message


Avatar for OMS.
OMS

Posts: 18919
Joined: 23 March 2004

Well Alan - as a conservative estimate in the absense of any firm data aim for Ib to be less than 0.4 x In

So in your case with a design current of 6.6A you'll want something like a 16A MCB

If you reduce your 1.8 to a more reasonable factor though, closer to actual running current you will have Ib of about 4A - so a 10A MCB.

You'll recognise this as a typical light commercial solution when used with 1.5mm2 cable - with a type C of course

Ideally you want inrush data for those ballasts - you can then determine what your peak current is and select a suitable breaker from there (allowing a crest factor).

Didn't you recently do 2396 - take a look in the electricians guide to calculations - Mr Cook explains it all in one of the later chapters

Regards

OMS

-------------------------
Failure is always an option
 28 November 2012 09:44 PM
User is offline View Users Profile Print this message



daveparry1

Posts: 5888
Joined: 04 July 2007

Or if it trips a "B", fit a "C"! Not a very scientific approach but practical,

Dave.
 28 November 2012 09:51 PM
User is offline View Users Profile Print this message



alanblaby

Posts: 283
Joined: 09 March 2012

Thanks all, yes, I did do 2396, and have got various books, but, of course, it is far easier to ask a question than to actually do some reading!
Yes, I'll have a look through the books tonight to understand the theory, I was going to fit a C type anyway, but wasnt quite sure on the need for it, and how to calculate it.

Thanks.
 28 November 2012 10:02 PM
User is offline View Users Profile Print this message


Avatar for OMS.
OMS

Posts: 18919
Joined: 23 March 2004

There is a section towards the end of the book Alan - it's a short chapter.

Basically you need the inrush current of the load.

from there you need to take the leading edge of the MCB characteristic so 3 x In for a Type B and 5 x In for a Type c and multiply that by a crest factor of say 1.404 - so for a 10A type C you have 10 x 5 x 1.404 = 70A

For a Type B it would be 10 x 3 x 1.404 = 32A

If the total inrush is less than 70A (or 32A) the MCB will hold against the inrush - if it's more the MCB will probably trip but remember it could actually be operating towards the trailing edge so not gauranteed that it will

Does that help ?

Regards

OMS

-------------------------
Failure is always an option
 29 November 2012 09:19 AM
User is offline View Users Profile Print this message



AJJewsbury

Posts: 10964
Joined: 13 August 2003

Needless to say you'll need to ensure that the lower Zs limit can be complied with (presuming no RCD) -- and check that the energy let-through of a C type won't exceed what the 1.0mm² c.p.c. will withstand (especially for faults close to the DB).
- Andy.
 29 November 2012 10:32 AM
User is offline View Users Profile Print this message



Jaymack

Posts: 4480
Joined: 07 April 2004

Originally posted by: OMS
multiply that by a crest factor of say 1.404


Really?

Regards
 29 November 2012 11:35 AM
User is offline View Users Profile Print this message


Avatar for OMS.
OMS

Posts: 18919
Joined: 23 March 2004

Originally posted by: Jaymack

Originally posted by: OMS

multiply that by a crest factor of say 1.404


Really?

Regards


Ahem - I think I'll need to check my typing - that should read 1.414 -


Regards

OMS

-------------------------
Failure is always an option
 29 November 2012 02:32 PM
User is offline View Users Profile Print this message



alanblaby

Posts: 283
Joined: 09 March 2012

Thanks all, yes the cable is pretty short so can cope with any VD/Zs/fault current etc. I found the relevant section in the IEE/IET calculations book, - all pretty simple, now I'm just about to ring up the manufacturer to get the inrush figures - clearly they dont think a 'typical' fitter will want to know, as the instructions, (if you can call them that) are quite sparse in their information.
Thanks
Alan.
 04 December 2012 10:01 PM
User is offline View Users Profile Print this message


Avatar for leckie.
leckie

Posts: 1605
Joined: 21 November 2008

My reply said time/current graphs. Isn't that correct? You need to know the load current,the starting current, and the inrush current. Each of the current demands must be within the lowest tripping current of the overload device.

I must admit I had never heard of crest factor until I read this post but I have now read the electricians guide that oms refered to.
 04 December 2012 10:39 PM
User is offline View Users Profile Print this message



AJJewsbury

Posts: 10964
Joined: 13 August 2003

My reply said time/current graphs. Isn't that correct?

Well, not the ones in BS 7671 anyway - as they only give the trailing edge (worst case for guaranteed disconnection) - whereas to avoid nuisance tripping you need to look at the leading edge. Manufacturer's data usually give both.

Even then the graphs aren't that helpful when you're considering the magnetic (instantaneous) trip of MCBs - at best they're just the vertical line bit. You can get just as much information from the multiplier for each type of MCB - e.g. 3x to 5x for a B type (again for avoiding nuisance tripping you'd want to keep the total inrush below the lower figure (with any adjustments for crest factor etc).

cable is pretty short so can cope with any VD/Zs/fault current etc

In terms of cables withstanding fault currents where MCBs are involved, faults close to the DB are the worst case!

- Andy.