Topic Title: EIC completion
Topic Summary: Supply parameters
Created On: 25 November 2012 12:38 PM
IanLloyd
When completing the 'Supply Characteristics and Earthing Arrangements' section of the EIC, for an industrial site with transformers supplying distribution and sub-distribution, what supply characteristics should be enetered? e.g. for a transformer supplying a switchboard #1 which then supplies a sub-distribution switchboard, #2, which in turn supplies a local distribution board, which supply characteristics should be entered for the local distribution board - those for the transformer/switchboard #1, switchboard #2 or the switch details supplying the DB (with whatever protective device parameters are fitted such as a fuse, MCCB or mcb etc.)?
 25 November 2012 12:56 PM
MrP
The supply characteristics at the origin must be recorded whether or not your coming off a board down stream
A photo copy of previous cert which contains supply characteristics stating where information obtained
On your cert it will say see attached sheet job done
MrP home in 24days but not counting
 25 November 2012 01:11 PM
Avatar for Robotman.
Robotman
Thats how we do it. The protective device for the downstreem boards is recorded on the test sheet later along with the ZE for that board.
 25 November 2012 02:00 PM
IanLloyd
Thought so, thanks both.
 26 November 2012 04:48 PM
Delbot321
Method of eaerthing directly off transformer will be TNCS (PNB) assuming they are the only customer off it. However the bonding requirements don't need to meet PME standard, just the same as all other earthing arrangements in the regs.
 26 November 2012 05:15 PM
Avatar for Parsley.
Parsley
UKPN's earthing manual states the customer's electrical installation requirements are exactly the same as for PME where PNB is present.