Hi

I have following issue to get clarified,

I installed a T5 lamp and measured earth terminal, voltage (without connecting the earth wire of the wiring system) wrt system earth it was 134V ( more than 50V)

(ballast is new and same value got for the another same brand ballast)

when I measured earth leakage current it was 0.3mA

Is it accepted the above voltage ?
 19 November 2012 03:21 AM
User is offline View Users Profile Print this message



crossy

Posts: 116
Joined: 14 February 2006

Since they likely have front end mains filters I would be surprised if a floating ground connection did not read around 50% of supply. Connect the ground and all will be well.
 19 November 2012 08:55 AM
User is offline View Users Profile Print this message



broadgage

Posts: 2325
Joined: 07 August 2007

Nothing remarkable at all.
Most class 1 appliances and components thereof such as lighting ballasts will exhibit broadly similar results.

This does however show the un wisdom of putting large lighting installations on RCDs.
At 0.3ma earth leakage per ballast, 50 ballasts would be about 15ma total leakage which is approaching the threshold of nuisance tripping of common RCDs.

Lighting circuits do not allways need RCD protection, but if this is required, it should be an RCBO per final lighting circuit, with perhaps no more than 20 ballasts per circuit.